    12/2 and 14/2 on 20 amp circuits
    Hello,
    I am helping my brother clean up and run a couple of new legs in his house, and I have encountered an interesting twist. The home runs are all 12/2 wire, but after the first connection, it usually will drop down to 14/2. All of the breakers are 20 amp in the sub panels. This house has clearly been this way since it was built in the late 80's. I thought the breaker could be no larger than the smallest wire in the chain. What's up? Thanks in advance
    Kendal
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Mar 25, 2009, 05:12 AM

    You are correct, should be on a 15 Amp Breaker.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #3

    Apr 13, 2009, 03:21 AM
    Quote Originally Posted by Stratmando View Post
    You are correct, should be on a 15 Amp Breaker.
    Looks like someone pulled a fast one on the electrical inspector!

    I'm a commercial electrician, and don't do too much Romex work, but the last house I wired the 14-2 Romec had a blue jacket, the 12-2 was yellow, and the 10 was red.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Apr 14, 2009, 03:12 PM

    If 14-2 is used for travellers, that circuit will be limited by a 15 Amp Breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

15 amp circuits [ 1 Answers ]

Hi, I am trying to decide whether to run another circuit. The living room is on a circuit 15 amp with 8 or 9 outlets and six ot seven ceiling lites. Is this too much? Can I continue this circuit into the dining area with another5 outlets and another four lites or do I need to run another...

Circuits [ 2 Answers ]

Suppose that the switch has been closed for a length of time sufficiently long for the capacitor to become fully charged. (a) Find the steady-state current in each resistor. R1=16.00 kΩ, R2=12.00 kΩ, and R3=2.00 kΩ. (b) find the charge on the capacitor. 9.00V, 10.0uC I found part (a) but I'm...

Circuits joined [ 7 Answers ]

Periodically I have a breaker trip in my service panel. When I go to reset, I always find that two breakers are actually tripped. Went and bought a meter and found that these two breakers are joined. (One of the two is turned off and I still get a full reading on both the Off and the on breaker)....

240 vac 60 amp circuits [ 3 Answers ]

I am installing 2 240volt 60 amp circuits for tankless water heaters. Do these neet to be run in a conduit? I am using #6 THHN which should be ableto handle 75 amps in this application.

GFI Circuits [ 1 Answers ]

All of my outdoor and garage electrical outlets have no power. I have reset all of the buttons on the gfi outlets. I f one outlet is bad,will they get no power? And how can you tell which one is bad?


View more questions Search