    240 vac 60 amp circuits
    I am installing 2 240volt 60 amp circuits for tankless water heaters. Do these neet to be run in a conduit? I am using #6 THHN which should be ableto handle 75 amps in this application.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Sep 12, 2007, 08:15 AM
    I'm confused: Two 60A services for a 75 A load? Why not a 75 A service?

    I do believe that the THHN would have to be in conduit.
    cmc21us's Avatar
    cmc21us Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 12, 2007, 09:27 AM
    I think my post was not specific enough. Each heater will draw about 54 amps at full load.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 12, 2007, 04:22 PM
    What does the manufacturer instructions state? What is the load in Kilowatts of each unit?

    You may have one circuit up to 120 amps to feed water heaters.

    But back to the questions.

    If your looking at Table 310.16, yes #6 THHN is rated at 75 amps in 90 Deg C column, however you may only use this column if the terminals at both ends of the circuit are rated at 90 Deg C.

    I know the breaker will only be rated at 75 Deg C, so you must use 75 Deg C Column so the #6 THHN must be protected at no more than 65 amps, or the next higher rating overcurrent device, which will be 70 amps.

    The circuit size must be rated at 125% of the load, 54 x 1.25= 67.5, so your breakers must be no smaller than 70 amps. See Section 422.10 (A) of the National Electric Code.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Convert 220 VAC 1Phase to 2-110VAC circuits [ 6 Answers ]

I have a 220VAC single phase 30 amp circuit that I would like to split into two 110VAC circuits. The 220VAC circuit has 3 wires and if I measure across the two main terminals I get the 220VAC and if I measure between a main terminal and what appears to be ground, I get the 110VAC. If I take one of...

Shared Circuits & New Bathroom Fan [ 2 Answers ]

My home was constructed around 1990. There are two full baths and one half bath. The bathroom receptacles share a dedicated 15A circuit (I have read that code now requires a 20A circuit) with a single GFCI outlet protecting all three locations. The vanity lights in all three bathrooms are on...

220 vac 100 amp service [ 8 Answers ]

What size of copper wire and conduit should I use for a 150' run to a sub panel?

Circuits allowed on a 15 Amp breaker - How many? [ 1 Answers ]

I just purchased a new townhome and have 13 wall outlets and 3 light switches on one 15 amp breaker. I wonder if that is within the electrical code? I have my PC, router, internet phone box, cable modem, portable a/c unit and of course other misc things such as lamps, camera and cell phone...

240 20 Amp double pole hookup [ 3 Answers ]

So this site is great, thanks Ok my next question is if I have a 12-2 wire at the baseboard then I would hook-up the dual-pole 20Amp at the box with both the white and black into each of the breakers connection and of course the ground to ground, no nuetral, right? Steve


View more questions Search