  • Mar 25, 2009, 05:03 AM
    1Kendal
    12/2 and 14/2 on 20 amp circuits
    Hello,
    I am helping my brother clean up and run a couple of new legs in his house, and I have encountered an interesting twist. The home runs are all 12/2 wire, but after the first connection, it usually will drop down to 14/2. All of the breakers are 20 amp in the sub panels. This house has clearly been this way since it was built in the late 80's. I thought the breaker could be no larger than the smallest wire in the chain. What's up? Thanks in advance
    Kendal
  • Mar 25, 2009, 05:12 AM
    Stratmando

    You are correct, should be on a 15 Amp Breaker.
  • Apr 13, 2009, 03:21 AM
    ohb0b
    Quote:

    Originally Posted by Stratmando View Post
    You are correct, should be on a 15 Amp Breaker.

    Looks like someone pulled a fast one on the electrical inspector!

    I'm a commercial electrician, and don't do too much Romex work, but the last house I wired the 14-2 Romec had a blue jacket, the 12-2 was yellow, and the 10 was red.
  • Apr 14, 2009, 03:12 PM
    Stratmando

    If 14-2 is used for travellers, that circuit will be limited by a 15 Amp Breaker.