    15 amp circuits
    Hi, I am trying to decide whether to run another circuit.
    The living room is on a circuit 15 amp with 8 or 9 outlets and six ot seven ceiling lites.
    Is this too much?
    Can I continue this circuit into the dining area with another5 outlets and another four lites or do I need to run another circuit?
    Thanks
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 19, 2008, 04:48 AM
    Most would say that circuit is already maxed out. Thing is what are you using on it. General use receptacles are an odd thing. You could have ten that never seen any use, yet one that gets used hard all the time.

    To answer your question, NO, you cannot extend this circuit into the DR for more receptacles. DR receptacles must be on a 20A circuit and not be combined with any other rooms than kitchen related rooms, such as the kitchen, pantry, breakfast nook, etc.
    Same goes for any lighting. You cannot have lighting combined with these "kitchen area" receptacles circuits.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuits [ 2 Answers ]

Suppose that the switch has been closed for a length of time sufficiently long for the capacitor to become fully charged. (a) Find the steady-state current in each resistor. R1=16.00 kΩ, R2=12.00 kΩ, and R3=2.00 kΩ. (b) find the charge on the capacitor. 9.00V, 10.0uC I found part (a) but I'm...

240 vac 60 amp circuits [ 3 Answers ]

I am installing 2 240volt 60 amp circuits for tankless water heaters. Do these neet to be run in a conduit? I am using #6 THHN which should be ableto handle 75 amps in this application.

GFI Circuits [ 1 Answers ]

All of my outdoor and garage electrical outlets have no power. I have reset all of the buttons on the gfi outlets. I f one outlet is bad,will they get no power? And how can you tell which one is bad?

Sub panel fed with two circuits [ 3 Answers ]

I was looking for space to add a circuit to an existing sub panel at my mother's house and ran into a problem that I need some advice on. Upon opening the sub panel, I discovered that it is being fed with two 12-3 Romex wires originating from two 20A circuits at the main. Now, I think that I...

New bathroom circuits [ 1 Answers ]

I am remodeling my 2nd floor bathroom and adding laundry (gas dryer). I replacing old circuits with 2 new circuits. One dedicated to washer/dryer and another for one outlet, 2 vanity lights, 1 general illumination light, and for the exhaust fan/shower light. Can I make one 12/3 run from my...


View more questions Search