    Emergency generator
    I would like to know if a 10,000-8,000 watt 50 amp emergency generator would power a Goodman 3 ton heat pump during a power outage. I don' know the amperage of the pump but is 3 ton units all the same. Would be very thankful for any helpful advice. lmg64
    Fr_Chuck's Avatar
    Fr_Chuck Posts: 81,301, Reputation: 7692
    Expert
     
    #2

    Feb 7, 2016, 11:02 PM
    The trouble will be in the starting amps, which is estimated at 75 to 85 amps depending on unit. The running amps is much lower at about 25.
    joypulv's Avatar
    joypulv Posts: 21,591, Reputation: 2941
    current pert
     
    #3

    Feb 8, 2016, 05:03 AM
    You should have all the specs for your heat pump written down and taped to the wall. Where's the documentation that came with it? Google the model and print it out.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting a three phase emergency generator to a transfer switch [ 4 Answers ]

Is it required to connect the neutral from the emergency generator to the neutral at the transfer switch.

Emergency Stop of Low-Speed 3.5 kW Generator [ 0 Answers ]

I have a 3-phase (with rectifier), 3.5 kW, 280 rpm generator. I want to have an emergency stop. A plain-old short is going to be too fast. I want something that will bring it to a stop in 2 - 3 seconds. What could I use?

10KW Emergency Back-up Generator [ 1 Answers ]

I installed a 10KW Back-up Elton Generator with an automatic switch servicing my entire 200A residential service. I realize that even under most circumstances that my service seldom exceeds 50% capacity. Now, the electrical inspector has requested a load calculation summary as to why I chose a...

What are emergency power backup & generator synchronization requirements for hospital [ 4 Answers ]

"What are the emergency power back up requirements & Generator synchronization requirements for a hospital requirements as per NFPA 70 & CIBSE.

Bryant Furnace won't start flame on my emergency generator [ 4 Answers ]

My newer Bryant plus 80 T gas furnace would not start the flame when it was connected to my emergency generator during an ice storm that caused the commercial power to go out. Is this a result of the poor power quality of the emergency generator which messed up the electronic circuits of the...


View more questions Search