    Connecting a three phase emergency generator to a transfer switch
    Is it required to connect the neutral from the emergency generator to the neutral at the transfer switch.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Sep 25, 2013, 04:30 AM
    ... "Required?" what if the load does not have a neutral?
    Typically yes, if the service has a neutral it needs to be connected through the transfer... Could the question be more specific?
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #3

    Sep 25, 2013, 10:41 PM
    Consider the earthing system of the installation(TT,TN-S,TNC-S etc)
    alpha1955's Avatar
    alpha1955 Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 26, 2013, 08:37 PM
    Quote Originally Posted by hfcarson View Post
    ..."Required?" what if the load does not have a neutral?
    Typically yes, if the service has a neutral it needs to be connected through the transfer...Could the question be more specific?
    The normal source provided by the utility company is a 3 phase 4 wire 240 volts, and its neutral is grounded at the normal source main disconnect. The transfer switch has an isolated neutral connection lug and the grounded neutral from the normal source service disconnect is wired to this lug. The emergency source (generator power) neutral is connected to the isolated neutral lug at the transfer switch, but there is no bonding connection from the isolated neutral lug to the transfer switch metal enclosure.
    I have several questions; do I need to bond the transfer switch metal enclosure to the isolated neutral lug? It is required to ground the chassis of the generator to a ground rod at the generator site or the neutral from the generator to the transfer switch isolated neutral ground is enough for grounding the generator chassis.

    Thanks for your help
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Sep 30, 2013, 04:14 AM
    In most cases the neutral of a service is only "grounded" or bonded to ground "once". There are a few reasons this "bond" should only happen one time. So unless the generator is a separately derived system, there should only be "one" bond. In this case the generator neutral and ground "should not" be bonded.

    If the generator is set up as a separately derived system, then you would bond neutral to ground and establish a grounding electrode system. The rules for this in detail are found in the electrical code articles 700, 701, 702 and 705 among others.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Generator Transfer Switch [ 1 Answers ]

I purchased a generator transfer kit that came with a 4 prong 30 amp cord that connects the generator to the transfer kit. The problem is that the outlet on my generator is only 20 amps. Can I remove the 30 amp plug and install a 20 amp plug leaving the 30 amp plug at the end that plugs into the...

Question regarding transfer switch for generator. [ 2 Answers ]

I have a 60 amp 10,000 watt generator and need to purchase a manual transfer switch, but what kind? I have a 200amp service and don't need an automatic transfer switch just manual. Could anyone tell me? Would a 60amp manual transfer switch be OK?

Connecting a 240 volt 20 amp duplex outlet on a generator to a 20 amp transfer switch [ 1 Answers ]

I have an older Coleman generator (5 KW) that a 240 Volt duplex outlet 20 AMP. I have a transfer switch rated for 5 KW that has a twist lock connector. How do I make a cord to go from my generator to the transfer switch without having to re-wire my generator? Thanks, Stan

Generator transfer switch [ 1 Answers ]

How difficult is it to install a generator transfer switch? It's pre-wired, doesn't look too Difficult. Is there anything I should look out for? The only thing I'm not sure of is it comes with two 15-amp 1-pole breakers, two 20-amp 1-pole breakers, and one 2-pole 20 amp breaker. How do I tell the...

3 wire 220 connecting transfer switch to generator [ 2 Answers ]

I have a manual transfer switch that I want to use between my house circuits and my 5000 watt generator. I have 3 wire #10 receptical existing from the circuit box over to where my generator sets (it is exhausted outside). Can I use this 3 wire line to connect my transfer switch to my generator...


View more questions Search