    Air handler and heat strip instalation
    I'm installing a new air handler (Goodman MBR 2000) in my home. I ordered a 15 kw heat strip kit (HKA-15C) to put in it. The kit has 2 breakers inside the air handler. (a 50 amp and a 25 amp) Instead of running 2 circuits with a #6 for the 50amp and a #10 for the 25amp they make a terminal block (SPW-01) to just run one circuit from the breaker panel to the air handler. I'm not sure if this just a terminal block, a power distribution terminal, or what so I'm trying to find out if I will need to run a larger wire than a #6 from panel to handler. a Guy from Hacy HVAC Supply has told me that all I need is the#6 and a 60amp in the breaker box. That the sequencers will rotate the heat strips where it won't ever pull more than 50amps. It seems like if I am using 15kw all three strips will be on together? I need to find out exactly what size wire and breaker I need to install the SPW-01 to keep me from running 2 lines. I don't want to run a #6 and find out it's not big enough. Would you please help me?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Jan 17, 2014, 01:02 PM
    What do the installation instructions say? This information is required to be there by law...
    ej36830's Avatar
    ej36830 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 17, 2014, 01:37 PM
    The installation instructions don't say anything about the wiring from the unit to the breaker panel
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jan 17, 2014, 03:44 PM
    Why do you say you need #6 AWG conductors?

    If that information is contained in the instructions, then certainly the OCPD, type of conductor and the temperature of the terminals should be give. It is required.

    For example a THHN (type) - 6 AWG (size) - 75(C) (terminal connection temp) can be used for up to 65 amps.

    From what I have read on the Goodman Manf. Site, it appears to me that the "Heat Strip" circuitry is managed by the internals of the air handler. In effect, one supply circuit is required to the unit from the panelboard.

    The installation of the heat strip does not require further changes to the electrical supply to the unit.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Jan 20, 2014, 07:07 AM
    Quote Originally Posted by ej36830 View Post
    The installation instructions don't say anything about the wiring from the unit to the breaker panel
    Are you sure? The installation instruction will typically list the "MCA" or minimum circuit ampacity... and also the "MOCP" or maximum overcurrent protection.

    When you find the above, then you can correctly size the wire and fuse or circuit breaker.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Jan 21, 2014, 06:52 AM
    I sent a note to Goodman. According to Goodman, a second 30 amp circuit is required for the heat strips.

    I strongly suggest that you contact an trained HVAC technician for additional information.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Use of 8/2 NM-B wiring for a 50amp Air handler 8kw heat strip 15 seer [ 0 Answers ]

If an NM-B 8/2 copper is used for a heat pump it should only draw high current when used in the winter for the 8kw heat strip. At that yime of the year the attic is very cold. Should this be considered when installing 8/2 NM-B with a fused down 60amp disconnect?

New ac with heat strip blows out cool air. [ 5 Answers ]

I recently (8 months)had a Fedders Ac System installed with a heat strip, but the heat does not seem to work properly. It blows out cool air and takes for ever to warm the house. The contractor has since moved to Dubai so I cannot get in touch with him. Is there anything I can check myself ?...

Cost of operation: gas furnace vs. Air handler with heat strip in Houston [ 0 Answers ]

Can anyone give me a rough idea of difference in cost between high-efficiency gas furnace vs. air handler with heat strip for Houston winters? Thanks,

Minimum Circuit Amps for 2 ton air handler with 5kw heat strip [ 2 Answers ]

Hi all. I currently have a 30Amp breaker on 10 gauge wire for the air handler and heat strip. This was a new install and the local inspector seems to think that 30amps is not enough. I took a picture of the specs and uploaded below. What breaker/wire is needed to be in compliance? Any help is...

Heat strip ina air handler [ 2 Answers ]

Where does the heat strip go in a air handler unit is. It in with the blower system


View more questions Search