Air handler and heat strip instalation
	
	
		I'm installing a new air handler (Goodman MBR 2000) in my home. I ordered a 15 kw heat strip kit (HKA-15C) to put in it. The kit has 2 breakers inside the air handler. (a 50 amp and a 25 amp) Instead of running 2 circuits with a #6 for the 50amp and a #10 for the 25amp they make a terminal block (SPW-01) to just run one circuit from the breaker panel to the air handler. I'm not sure if this just a terminal block, a power distribution terminal, or what so I'm trying to find out if I will need to run a larger wire than a #6 from panel to handler. a Guy from Hacy HVAC Supply has told me that all I need is the#6 and a 60amp in the breaker box. That the sequencers will rotate the heat strips where it won't ever pull more than 50amps. It seems like if I am using 15kw all three strips will be on together? I need to find out exactly what size wire and breaker I need to install the SPW-01 to keep me from running 2 lines. I don't want to run a #6 and find out it's not big enough. Would you please help me?