    Goodman furnace problems
    80% goodman furnace. There is no a/c with this unit. New high limit switch. Furnace runs a complete cycle, but blower motor stays running. t-stat new, wired right. Blower housing clean. Return air might be undersized, a little. Will jumping low limit tell me anything? Do not know flash code.
    dewey066's Avatar
    dewey066 Posts: 49, Reputation: 1
    Junior Member
     
    #2

    Sep 19, 2013, 07:00 PM
    First of all is the thermostat set for fan-"Auto". If it is "On" then it will run constantly. Some thermostats have a switch, some are a little more fancy.

    Is this a mechanical fan/limit control (once you take cover off there is a "dial" with three adjustable set-point tabs) or a simple limit switch along with a roll-out switch? Is this oil or gas? The mechanical control's first set-point tab is fan-off (the second tab is fan-on, and the third is the limit which will kill power to the burner, but keep the blower running). Is this set too low? Does it eventually stop?

    If there is not a fan/limit control then I am assuming that the blower is energized by some type of electronic circuit board. Are there LED's on the circuit board? Does it show that the "W" is lit (this is what makes the call for heat). If it is a timer board then you can try carefully pulling off the W wire wire (low-voltage). The blower should stop after a delay. If this is the case then it could be a bad board.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace problems [ 1 Answers ]

I have a Goodman GMNT080-4 gas furnace. It stopped working and in checking it out, the control board was corroded, due to moisture ,and some of the dioids ends were rusted and broken from the sodder . I replaced the control board (B18099-13), but it still would not work. I have power to the board,...

Goodman furnace problems [ 1 Answers ]

The system comes on, the igniter glows, the burners light, and the fan comes on. Why does my system cycles on and off? The error code is for 4 flash. I replaced the limit switches. The system still cycles on and off. Why?

Goodman Furnace Problems [ 3 Answers ]

Hi My Furnace Starts and everything then it stops, then it repeats this process over and over what's wrong with it? I have a Goodman furnace, its relatively new the house was built in 2002. Please help it just snowed! IM FREEEZING :( what's wrong with it is it the ignition lighter thing?

Goodman furnace problems [ 3 Answers ]

Goodman furnace won't come on light blinks 6 times and the blower motor run continueous.

Goodman furnace problems [ 3 Answers ]

Son in law has a Goodman natural gas furnace. No heat. LED is flashing 4 times ('Upper limit open' is the message associated with this error). The blower motor turns on, the exhaust motor (I think that's what it is) turns on for about 10 seconds then turns off. Tried changing the air filter (was...


View more questions Search