    Goodman furnace problems
    Son in law has a Goodman natural gas furnace. No heat. LED is flashing 4 times ('Upper limit open' is the message associated with this error). The blower motor turns on, the exhaust motor (I think that's what it is) turns on for about 10 seconds then turns off.

    Tried changing the air filter (was very dirty) but that didn't help.

    Any other ideas? I don't have the full specs for the furnace right now.

    Thanks,

    Freezing in the north
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 7, 2009, 09:10 AM
    Reset upper limit control. Wiring diagram on back side of blower door. Something caused this safety item to trip and that might have been the dirty air filter. Look for reset button in center on control. If it will not reset replace.
    Frozen09's Avatar
    Frozen09 Posts: 1, Reputation: 1
    New Member
     
    #3

    Dec 7, 2009, 12:39 PM
    I went back to my son in laws to do more checking this morning and brought my meter. I found that the main limit control thermostat had indeed opened up (probably because of the dirty filter decreasing the air flow) and had not reset (and there was no reset button on it). As a temporary solution, I just gave the thermostat a sharp tap to reset it and it closed again so that the furnace could turn back on. Will get a new thermostat to replace that one. AND told them to replace the filter on a regular basis!!
    Thanks for your reply hvac1000.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Dec 7, 2009, 01:09 PM
    Replace with same value. Glad you got the heat going since it is getting cold out there.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace problems [ 21 Answers ]

Hi - I have a Goodman GPM furnace. It works intermittently. I replaced breaker, thermostat, Control board and surface igniter. All appears well on start up sequence ; blower runs and igniter heats up and then turns off as no gas comes out. Control board codes says OK. Can anybody recommend what to...

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

3 yr old Goodman Gas Forced Air Furnace problems [ 10 Answers ]

If thermostat is set to 70-90 degrees the furnace burner and blower will run constantly and the temp never gets above 68 degrees in the house. I have a Lux programmable thermostat and was thinking of replacing it with a Honeywell. I have a new filter. Any ideas? The weather has been in the...


View more questions Search