    Basement wiring
    Lots of questions. Finishing a basement with a bathroom, bedroom and a family room.

    Are GFI circuit breakers or outlets needed in the basement family room?

    Arc fault breakers are required in bedrooms only and are gfi's required in a basement bedroom?

    Running a 20amp separate circuit for the bathroom, can you run the main power to the GFI, then to your other outlets (within the bathroom), then to the light switch and fan? And will this make the fan and light gfi protected?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 5, 2007, 03:39 AM
    Only outlets in a unfinished basement need to be GFI, once it is finished off to a room, the outlets can be standard .

    Yes AFCI protection is for bedrooms only, including lights and the smoke detector. Should check with local code as some states have waived the smoke detector on AFCI and do not require, or allow, it on AFCI.

    The bathroom outlet needs a 20 amp circuit, and GFI, the lights in this one bathroom can be on the same outlet circuit, but do not need to be GFI protected. To connect the lights and fan without GFI protection, simply splice onto the feed to the Line side of the GFI outlet. Best to not GFI protect the light at least so you still have lights if the GFI trips.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement Wiring [ 4 Answers ]

Hi, I'm currently wiring my basement soon which is about 1000 square feet. It will include a family room, a bedroom and a bathroom. I currently have one 15 amp 14/3 circuit running down there connected to one circuit breaker from the main panel. I've calculated that I need a total of 2 15 amp...

Wiring basement [ 1 Answers ]

I am using metal studs in my basmsnt. I positioned each outlet 18inches on center from floor. I purchased the grommets and am ready to start fishing the wire. Can I use the hole in the stud located 5 inches lower than each outlet location in order to save wire? That is, the next available hole...

Wiring basement lighting [ 1 Answers ]

I am wiring a basement for ceiling lights. I have not purchased fixtures yet and we want submerged lighting. My basement is rather small and I have decided to put up 8 fixtures and they will be switched on and off with (2) 3way switches one at top of stairs one at bottom. They breaker panel is new...

Wiring basement [ 2 Answers ]

I am wiring a finished basement. The problem is the main panel is in the Gar 200a service. This is abour 65 ' away from the finished basment. I was going to run 2 20 amp breakers for the basement room.. it will have lites, frig, entert. Center etc. My question is I want to run a 50 amp...

Basement wiring cost [ 1 Answers ]

I know this a very vague question, but ball park figure, how much should it cost to have a professional electrician fully wire a basement being finished? I was quoted $1700 and thought it was very high?


View more questions Search