    Wiring basement
    I am wiring a finished basement. The problem is the main panel is in the Gar 200a service. This is abour 65 ' away from the finished basment. I was going to run 2 20 amp breakers for the basement room.. it will have lites, frig, entert. Center etc.
    My question is I want to run a 50 amp breaker with #8 wire the 65' into a sub panel and then the 3 20 amp breakers or should I use # 6 wire.. or even run a double 30 with #10 into a sub panel and then the 20's..

    Any input would be great.. thank you in advance..
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 28, 2006, 06:24 AM
    #8 copper wire THHN / 75Deg C rated insulation for a 50 amp circuit at 70 feet is fine.


    If you use #6 wire, then you can use a 60 or 70 amp circuit breaker as the feeder.

    A larger feeder/subpanel will gve you more capacity n the future.

    I think the 30 amp feeder/subpanel is cutting to close. Because the distance is so long, will be easier for you to run the #8 or # 6 cable once and be done with it.
    pelle's Avatar
    pelle Posts: 96, Reputation: 0
    Junior Member
     
    #3

    Sep 28, 2006, 01:40 PM
    Thank you for your advice..

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement Wiring [ 4 Answers ]

Hi, I'm currently wiring my basement soon which is about 1000 square feet. It will include a family room, a bedroom and a bathroom. I currently have one 15 amp 14/3 circuit running down there connected to one circuit breaker from the main panel. I've calculated that I need a total of 2 15 amp...

Conduit requirements for basement wiring [ 1 Answers ]

I am finishing a basement with stud wall and dry wall. Is there any need for conduit to carry the wires behind the dry wall? I know for an unfinished basement wiring below grade must be in conduit but must it if the walls are finished? Thanks Dschaar

Basement wiring cost [ 1 Answers ]

I know this a very vague question, but ball park figure, how much should it cost to have a professional electrician fully wire a basement being finished? I was quoted $1700 and thought it was very high?

Basement wiring (question of separate circuits) [ 15 Answers ]

Hi, I will be wiring my basement soon (about 1400sqf) with one family/TV room, a bedroom, an office and a bathroom. They ran only one 15AMP circuit that currently operates basement lights (8 of them) and 2 GFI outlets. They also put each bedroom upstairs on a separete circuit breaker with a...

Wiring with 15 amp [ 1 Answers ]

In some work on my house, I noticed a light had 20 gauge wire feeding it from a 14 gauge line. The breaker on the 14 gauge is 15 amp. Is this type of hookup OK?


View more questions Search