    Basement Wiring
    Hi,
    I'm currently wiring my basement soon which is about 1000 square feet. It will include a family room, a bedroom and a bathroom. I currently have one 15 amp 14/3 circuit running down there connected to one circuit breaker from the main panel. I've calculated that I need a total of 2 15 amp circuits(some of the lights and some of the receptacles) and 4 20 amp circuits (1 for the bathroom, 1 for treadmill, 1 for the electric fireplace and the last for the remaining lights and receptacles). For the 15 amp circuits I used the original 14/3 coming in from the main panel and added another 14/2 to handle the additional 15 amp circuit.

    My question is: Can I have two runs of 12/4 from the main panel? Each run having two 20 amp circuit breakers and sharing a common ground (giving a total of 4 new 20 amp breakers at the main panel). Is this OK as it will allow me to pull only 2 wires from the main rather than 4.

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 12, 2006, 01:25 PM
    Ok , first of all, I assume when you say #14/3 cable, you mean a cable with a black, white and bare wire. We do not count the bare ground, it is understood, so I will be calling it a 2 wire, or a black, white, and red will be a 3 wire.

    All 120 volt lights and outlets in the bedroom will need an ARC Fault circuit, so may be 15 or 20 amp but must use a 2 wire, because you need to use a ARC Fault circuit breaker, and cannot use a shared neutral.

    The bathroom requires a 20 amp circuit, if it is the only bathroom on the circuit then any light or fan in that room can be on the same circuit. There must be an outlet at the sink on that circuit, and the outlet must be a GFI.

    A 20 amp circuit for the treadmill is good, the remaining family room outlets can be either all on a 15 or 20 amp circuit.

    The fireplace does not need a circuit by itself, can be on any circuit.

    So you will need:
    1-#12-2 for bathroom (if you use a 3 wire, then you can have a spare circuit)
    1-#14-2 or #12-2 cable for all bedroom lights and outlets.
    1-#12-3 for black family room and red for treadmill
    1- existing #14-3 for family room lights

    Now you also need smoke detectors, AC with battery backup, and interconnected with each other and with any existing interconnectable smoke detectors.

    One smoke must be in the bedroom, and one other one needs to be anywhere in the other rooms, usually in a central location of the general area. The smoke detector in the bedroom must not be connected to or affected by the ARC Fault breaker.

    I am curious how you did calculations, can you explain? Also, I trust you will be checking with your local municipal building official to be sure you can wire this yourself, with a permit , of course. Then you can ask about any local codes tha must be followed as all I can comment on is National Electric Codes.

    Hope this helps.
    ssnook's Avatar
    ssnook Posts: 4, Reputation: 1
    New Member
     
    #3

    Feb 4, 2011, 02:54 PM
    The smoke detector in the bedroom must not be connected to or affected by the ARC Fault breaker.

    NOT True
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Feb 4, 2011, 07:35 PM
    I wouldn't use MWBC in my home... just not a good idea for residential applications. You effectively lose two circuits with a breaker tripping, and should you have a neutral come loose you could experience more serious problems with excessive voltage.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Feb 5, 2011, 04:47 AM
    SSnook, this post is from 2006.

    The Code in effect now is 2008 edition, and that requires the smoke detector to be Arc Fault protected.

    However, some states. Maine for example, have taken exception to that requirement and do not want the detector Arc Fault protected.

    Please refrain from answering questions older than a few months.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring [ 3 Answers ]

Hi, I;m new to the home owneship family, but I recently tried to install a HB Tahoe 52". The fan and light kit wires are blue, white and black. My ceiling wires are red, black and white. I have blue and red together, white to white and black to black. Only the lights work, what did I do wrong?

Conduit requirements for basement wiring [ 1 Answers ]

I am finishing a basement with stud wall and dry wall. Is there any need for conduit to carry the wires behind the dry wall? I know for an unfinished basement wiring below grade must be in conduit but must it if the walls are finished? Thanks Dschaar

Basement wiring cost [ 1 Answers ]

I know this a very vague question, but ball park figure, how much should it cost to have a professional electrician fully wire a basement being finished? I was quoted $1700 and thought it was very high?

Basement wiring (question of separate circuits) [ 15 Answers ]

Hi, I will be wiring my basement soon (about 1400sqf) with one family/TV room, a bedroom, an office and a bathroom. They ran only one 15AMP circuit that currently operates basement lights (8 of them) and 2 GFI outlets. They also put each bedroom upstairs on a separete circuit breaker with a...

Wiring [ 1 Answers ]

Sorry, I was tired when I posted the last thread. I meant to say a light was being feed by a 12 gauge wire from a 14 gauge line with a 15 amp breaker. Is this OK?


View more questions Search