    If you have the typical 400 amp service with two 200 amp disconnects on a panel for your service and you have installed your 5/8 copper ground rod and installed the solid copper wire to the meter panel should you also run a solid ground wire from each disconnect panel to the meter panel ? The meter panel and the two disconnects are mounted on a wooden panel and connected together with electrical rated pvc conduit
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 24, 2010, 03:53 AM
    No ground wire is needed between the meter and the two disconnects.

    The neutral bar in the enclosure that contains a disconnect(s) must be bonded to the metal can of the enclosure. The grounding electrode conductor from the ground rod(s) can connect to the neutral either in the meter or at the disconnect(s).

    From the disconnect(s) to the circuit breaker panelboard(s) will need an equipment grounding conductor.
    dgley's Avatar
    dgley Posts: 4, Reputation: 1
    New Member
     
    #3

    Apr 25, 2010, 12:59 AM

    Thanks tk russell

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp disconnect [ 1 Answers ]

Will a 200 amp single phase disconnect have two 100 amp fuses or two 200 amp fuses?

200 amp safety disconnect vs. 200 amp breaker [ 1 Answers ]

I am in the planning stages of installing an automatic transfer switch for my house-Asco 225 amp". While doing this I was going to upgrade my 100 amp service to a 200 amp service. I was also thinking during this upgrade I would like to have some sort of disconnect between the meter and my automatic...

INstall 200 amp disconnect [ 1 Answers ]

From my 200 amp meter socket to my 200 amp disconnect, does the wires go to the top of the 200 amp breaker or the bottom or does it matter?

200 amp breaker/disconnect [ 2 Answers ]

I'm needing wiring help. I am wiring a mobile home and at the service pole I'm not wanting to hang the 200 amp breaker box since it's over one foot long and would like to hang a much small box w/ only a lone breaker or disconnect before going to the 200amp breaker panel mounted else where. ...

Need help with 200 amp disconnect [ 1 Answers ]

I am in the process of re-wiring my house. My load center used to be located on the outside of my house. I have now moved the load center (200 amp sq d qo panal) to the inside, and am looking to place a 200 amp disconnect next to the meter pan. I was told I needed to get 2 awg 3 cond with ground to...


View more questions Search