    Toilet vent
    When I had my house built, I had the contractor rough in plumbing for a basement bathroom. I have a bi-level house so when I was going to install the toilet I noticed that there was a pipe hanging out of the basement ceiling above where the toilet is going. Since the piping was already installed and under the concrete floor does this mean I am going to have to dig the floor up to connect the vent to the toilet drain or is there another vent hooked up some where else on the drain line
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Mar 29, 2009, 09:08 AM
    This will depend upoon where you live and the code you fall under, Do you live on the West Coast? UPC mandates that each fixture be vented so if you fall under OPC Code then that just might be the vent for the toilet. What size is the pipe hanging out of the ceiling? On the other hand this could very well be the lavatory vent and if you live in the other 980% of the country your toilet may already be wet vented.
    Let me show you a typical, (in my area) bathroom group rough in. This configuration only uses one vent for the entire group.
    4" ,(under cement and basements) 3" (on first and second floor) from the toilet to the main. The lavatory to connect to the toilet drain line and vent to the roof or revent back in the attic to a existing roof vent. The tub/shower to connect to the lavatory drain line and be wet vented by it as will the toilet. Be advised to always check local codes before changing or remodeling your drainage system.
    As I said, It all depends on where you liive and the code you fall under Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to vent toilet [ 1 Answers ]

I am adding a half bath on the 2nd story. The toilet cannot be vented at the back wall of the toilet due to the roof configuration. Can I put in a wye fitting at the 3 inch waste stack just below the floor joist and run my 2 inch vent about 4 feet horizontally in the joist bay where I can then go...

Toilet vent [ 1 Answers ]

I am remodeling my bathrooms, I knocked out a wall to combine a smaller bathroom and a larger bathroom. When I knocked out the wall I found the toilet vent that goes through the ceiling of the bathroom and out through the roof. It is located about 8 inches from the outdside wall and I really...

Toilet Vent [ 1 Answers ]

A house requires one 3" main vent. On new construction we usually make this vent the kitchen sink vent6. The rest can be 2". You have a major fixture discharging past two unvented minor ones. Both the shower and the tub will have to be vented individually, the vents will have to be installed Just...

Toilet vent [ 2 Answers ]

I am looking for a way to clean out a possibly blocked toilet vent. I have a drop in water in the bowl and when doing laundry, I sometimes get a gurgle and the smell of sewer gas. I am having the septic pumped and I also tries flushing out the vent with a water hose, not an easy task. Any...

Toilet Vent [ 5 Answers ]

I am putting in a septic system at my cabin, there is a toilet in the bathroom that will need to be tied to this new septic system. The toilet has a 4" pipe that runs through the crawl space, under the footings and is stubbed outside the cabin. This pipe is a straight pipe with total of about 13'...