    Subpanel with a long run.
    Hi,
    I want to run electric to my utility shed. I was thinking 60 amps. There is one problem. The shed is about 250 feet from my house. I plan to run the wire under ground. So now for the questions:
    1. What gage wire?
    2. Should I in case the wire in PVC, or use underground wire?
    3. How deep?
    4. Can I run other wire (phone, cable, two way switch) in with the service wire?

    Thanks
    Mark V
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 25, 2008, 03:23 PM
    1) A 60A feeder would require #6cu if in conduit. Depending on the calculated load you might want to upsize to #4 because of the distance.
    You will need two hots and a neutral of the same size. The ground can be #10 if you run #6, or if you run #4 the ground must be #8.

    2) I would use conduit all the way. PVC sch40 for underground and PVC sch80 for exposed sections.

    3) At least 18".

    4) NO! You need separate conduits for those.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

60 AMP Subpanel Help [ 6 Answers ]

I would like to install a 60 amp subpanel. I plan to have a 60amp breaker in my main panel fed to a main lug subpanel. Questions: Can I use 6/3 Romex NM - the distance is about 65 feet? Can I use a 100amp main lug sub panel even though the main breaker is 60amps? I need four spaces in the...

100 amp subpanel [ 1 Answers ]

I am connecting a 100 amp subpanel from my main panel on my home to be used in my new garage that is 155 feet from the house. The main panel is a 200 amp combo box on the outside of my house that supplies a 200 amp panel inside my house. I have been told that I may use mobile home feeder 2-2-2-4...

What to buy for subpanel [ 3 Answers ]

Friend installing a subpanel for me. Need to know what to buy. 250 feet from house. 4 wire all aluminum #2 in conduit under ground.Not hooked up at barn or house yet. Just cable ends ready to go. Was given a 100 amp square D 6 spaces box. DO I need a main shut off in the barn? Will this box work?...

Long distance subpanel wire size [ 7 Answers ]

I have a horse barn that is 1014 feet of 1.5" conduit away from the main house panel. The main panel is 400 amp 240/120 volt and I have left 100 amps for use in the barn. My current electrical needs in the barn are 2 - 1/2hp motors, one for a gate and one for a hot walker, and a small fridge that...

MLO subpanel? [ 2 Answers ]

Hi, I just posted this as a reply in an existing topic, but perhaps I should also post it here in its own new topic? I'm not sure. ... I'm doing a major renovation on my house and what I have had here is a 40 position 200 amp main panel. An electrician told me I need to have a sub panel...


View more questions Search