    Long distance subpanel wire size
    I have a horse barn that is 1014 feet of 1.5" conduit away from the main house panel. The main panel is 400 amp 240/120 volt and I have left 100 amps for use in the barn. My current electrical needs in the barn are 2 - 1/2hp motors, one for a gate and one for a hot walker, and a small fridge that is rated at 1.3 amps, a tankless hot water heater rated at 1.04 amps and a total of 3000 watts of inside and outdoor lights. All loads are 110 volts. What would be the most economical way to run wire to the 100 amp subpanel. I know the load is much less than what the panel is rated for, but I would like to allow a little room for future expansion. I have been exploring boost transformers, trying to keep the wire size smaller and cheaper. Please make your suggestions specific with model numbers and wire sizes including a ground wire size. Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 22, 2007, 05:06 PM
    Wow, is your barn in the next county? It may be cheaper to move the barn.

    All kidding aside:

    I added your loads, rounded the numbers up, I arrive at a balanced load per leg of 25 amps each 120 volt leg. Doubling that to 50 amps per leg to allow for future expansion, using a 400 MCM Al wire will produce a 3% voltage drop, which is the maximum recommended allowable voltage drop for a feeder.

    Here is a website that lists 3 wire URD cable, however, no 400 MCM, the next size up is 500 MCM, which will help with additional future load and reduced voltage drop.

    Aluminum URD Cable- 600V- Triplex 90°C For Direct Burial on Custom Cable Corp.


    I am not sure the cost of this cable. Best for you to find a local supplier that can access and price the product.

    With this you can compare the cost to using transformers. To provide for an 80 amp load, you will need two 25 KVA single phase transformers with 480 volt primary and 120/240 volt secondary. These can cost approximately $700.00 each.

    See the attached catalog page from the website:

    Acme Electric Corporation Product Catalog

    Using these two transformer, you can reduce the wire size to #2/0.

    Along with the cost of transformers will need to add the cost of circuit breakers for both primary and secondary protection of both transformers, allow $200.00 for two 250 volt disconnects and $400.00 for two 600 volt disconnects.

    As long as there is no other metallic paths between the two buildings, you can use the 3 wire feeder method, and drive ground rods at the subpanel at the barn, and connect the neutral and equipment ground bar together at the subpanel. If an equipment ground wire is run with the feeder, ground rods are still needed at the subpanel, however, the neutral and equipment ground would not be connected together.

    You will need to compile a bill of material for both plans to see which is the less costly. I think you may find just using the larger #500 MCM cable without the transformers will be the least expensive.

    I hope this helps, this is quite a project to design ,layout and price, never mind install.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Aug 22, 2007, 07:44 PM
    I'm with tk on this!

    Is there any utility power closer to the barn?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 23, 2007, 04:22 AM
    Hey Washington! Where you been, month long vacation? About time you get back here. Missed you.
    NoEnuf2bAdanger's Avatar
    NoEnuf2bAdanger Posts: 3, Reputation: 1
    New Member
     
    #5

    Aug 23, 2007, 10:06 AM
    Thanks for the info. There is no utility power any closer than my main panel.
    NoEnuf2bAdanger's Avatar
    NoEnuf2bAdanger Posts: 3, Reputation: 1
    New Member
     
    #6

    Aug 23, 2007, 10:34 AM
    I looked up the cable you mentioned TK. It has an OD of 2.03" and I only have a 1.5" conduit. I know I could direct bury it, but would rather not for ease of replacement if there ever was a problem. The cost was $5888 per 1000 feet.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Aug 23, 2007, 01:37 PM
    I figured this cable would be costly, but not that much. Price out the transformer method, looks like that may be cheaper. As far as the 1-1/2" conduit, it is too small for either method.

    Let us know what you decide to do.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #8

    Aug 24, 2007, 03:39 PM
    Was on vacation for two weeks.

    Thanks for the welcome back! :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Long distance [ 3 Answers ]

I'm usually on here giving advice, but here I am needing some. I'll make it sweet and simple. I am moving due to financial reasons and will undoubtedly improve my situation once I move to my new location. She's staying but she really has no ties to where she currently lives as she's moved from...

The long distance or is it him? [ 2 Answers ]

I'm sorry if this story is long but the background is important. -------------------------------------------------------------------------------- I am 25 years old and my ex is 27. We met in the first year of law school and then he moved five hours away for school. Before he moved away, I got...

Wire size selction for a subpanel [ 1 Answers ]

A family member has built a small (12X20') home shop for welding projects. A subpanel fed from the 225A home breaker panel will be used to feed a subpanel in the shop. Installed, the subpanel feed wire will entail a total run of circa 110 feet. Query: What is the correct size wire for this...

4 wire home service entrance wire size [ 1 Answers ]

Mobile home requires 4 wire electrical service entrance wire. Distance is 160 foot from meter to breaker panel. 220V service. What size wire do I use? Can I use diff. size for neutral and ground?


View more questions Search