    MLO subpanel?
    Hi, I just posted this as a reply in an existing topic, but perhaps I should also post it here in its own new topic? I'm not sure.

    ...

    I'm doing a major renovation on my house and what I have had here is a 40 position 200 amp main panel. An electrician told me I need to have a sub panel next to that to deal with all the circuits I'm adding. Its not that any of them will have anything big here or there, but for convenience I have made many little circuits (for example, a separate one for microwave in kitchen, etc)

    I want to put a subpanel next to the main one and have hopefully 40 more circuits to be able to cover everything in the house...

    The electrician told me to get a MLO for this... and so I'm assuming to put something like a 100-125-150 or so amp breaker in the main panel and feed to the subpanel next to that... that part makes sense... but what I'm confused by is this part where I have to isolate the neutral bar from the ground bar... could you explain that to me a little bit? Basically I have a murry 200 amp main panel right now... if I purchase a 40 position murry mlo box, how should I connect the two? Then can I just have a bunch of 20 amp circuits on that?

    -Dave
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jan 31, 2007, 08:25 AM
    Dave, how much did you advising electrician say he'd charge to do this for you? I do stuff like this all of the time. My rule of thumb for home owners is 110 V is worth a try, 220 V you could die.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Jan 31, 2007, 10:07 AM
    Once you take the cover off the main panel, you may as well be installing a 2 pole breaker as a single one, which is the difference between 120 and 240. The older panels had one buss for grounds and neutrals. Current code calls for separate ones although they are connected at the main panel only. So you will be running 4 fat wires to the sub panel. The 2 hot ones run from a double pole breaker to the main lugs.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical Subpanel [ 1 Answers ]

I want to install a electrical subpanel(~50 amp) in my garage, if I do not feed the subpanel with a breaker from the main service of the house,would or could I tie into the main lugs of the main service to feed the subpanel? (Using the proper wire size) Would I have to use a ground rod for the...

Installing a Subpanel [ 3 Answers ]

I'm setting up a woodshop in my garage and want to install a subpanel to run my equipment off (it's going to be right next to the main). I'm starting from scratch, knowing extremely little about how to accomplish this. What sort of box do I need to buy, how do I size the breaker that will feed...

Grounding a subpanel [ 1 Answers ]

I have a set of direct current solar panels mounted on a metal structure (carport). All the panels and the structure are grounded to a ground rod driven near one of the support posts. Can I use the same ground rod for the ground connection of an alternating current subpanel mounted on one of...

Some subpanel questions [ 1 Answers ]

My winter project is to build a 12x20 shed in the far corner of the back yard. I'd like to run electric service for lights and power tools. On the outside of the house about 30' from the main panel I have a 240V pullout switch that at one time supplied an AC compressor (since relocated to the...

Adding subpanel [ 1 Answers ]

I'm converting my garage to a woodshop, so I need 220 service for the table saw and band saw, and potentially later the dust collector and compressor. Also I want to run a new circuit for lights, plus two 110 outlet circuits. That's a possible four 220 and three new 110 circuits. I've got a...


View more questions Search