    Heat Overload
    First off I have 3 heating zones in my home, gas fired boiler and hot water baseboard. My issue is two fold.

    1st issue... thermostats work fine on both floors and with that in mind I keep the temp set at 72 on the first floor and for some reason this heats the baseboards on the second floor as well and I cannot figure out why this is happening I keep the thermostat on floor 2 off because of this, and if I do kick on the thermostat on floor 2 it becomes unbearable. Any reason why this is happening?


    2nd issue... sort of the same as the first, I finished off my basement and added a new digital thermostat in the basement and I cannot use this one in the basement because it make the second floor unbearable.

    Any info you could provide would be greatly appreciated, as I am on the verge of having the entire rewired in the fear that the zones are wired incorrectly.

    Is this a common issue


    jag82899
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 23, 2008, 01:14 PM
    You have a valve (s) problems. Wiring problem or a thermostat problem. The piping should also be checked so as to figure which zone is fed by which valve and the reason for line feed back.This problem will have to be checked on site as there is no way we can check the work here. At least you now have something to go on.

    Not a common issue.
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #3

    Jan 23, 2008, 05:44 PM
    You are experiencing "Ghosting". It is caused by heat excaping when a zone calls for heat and the check valve on the second floor is allowing water flow. If you can follow your piping to see which ones serve the second floor, find the check valve and tap it a few times. Also check to make sure only the zones calling for heat are getting heat. Yes, you could have some crossed wires.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Emotional overload [ 98 Answers ]

My ex just recently graduated from the NYPD academy, something he'd been in college for while we were dating. Now, he's out on the streets patrolling, and I know contacting him is a bad idea, so I'd like to write out how I feel here. For one thing, my dad told me the other day that he sees my ex on...

Why does a condenser fan go off on overload [ 2 Answers ]

I put in a brand new fan motor & capaciter that matches perfectly with the one I removed But it goes off on internal overload after 5 minutes. What could be my problem!

How much to overload a circuit [ 1 Answers ]

Hi I will try to give as much information as I can and be as clear as possible I'm definitely a novice when it comes to this stuff and having just moved to the US from overseas (lived in the world of 240v and AC or was that DC ;) ) I'm struggling a little. Anyway the question. I have started...

Burnt hardrive overload [ 1 Answers ]

My hardrive was replaced due to burnt hardrive overload now its fixed and we cannot retrieve our emails or send from msn messagener coud you please advise us on how we can do so thank you tazannehillier

Circuit Breaker Overload [ 1 Answers ]

I have just installed Heat Tape on my roof to deal with ice damming that has started to take place on my roof (no Cold Roof and I live in Wyoming on a North Facing Slope) Anyway, to plug in the heat tape, I converted an old light fixture into an outlet, and hoped that my problem would be fixed. ...


View more questions Search