    Double taps at electrical panel
    I have just had a home inspection on my home. The inspector said that I had several double taps. Can these be corrected without adding breakers. The 200 amp panel is almost full.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 26, 2007, 10:58 AM
    There are three ways that the problem can be corrected:
    1) Add a subpanel
    2) Replace single breakers with tandem breakers
    3) Pigtail the connections

    1) The subpanel requires a large circuit breaker in the main panel. In the sub-panel ground and neutral are isolated. You usually have to purchase a ground bar kit and it will not have a main breaker.

    2) A tandem breaker has two independent circuit breakers in a single slot. There is a label on the panel which specifies the number of "poles" the panel can have. This cannot be exceeded. A "pole" might be defined as the number of places to connect circuits.

    3) Circuits can be pigtailed. A short length of wire connected to the two circuits wirenutted together.
    happyguy's Avatar
    happyguy Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 26, 2007, 12:09 PM
    Comment on KISS's post
    Exactly what I needed
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 26, 2007, 12:22 PM
    Before adding too many tandem breakers, read the fine print on your box label about how many poles you are allowed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical panel conductors [ 2 Answers ]

What size copper conductors do I need for a 200 amp panel approximetly 150' form the pole. Thank You, Brian

Electrical Panel [ 1 Answers ]

How many watts can go on a circuit that is 2 x 20 = 40 amps?

Double taps and splices [ 1 Answers ]

I have a panel that is outside with a 110 receptacle attached directly to the panel. I want to add a two more receptacles to this circuit for a total of 3 receptacles. What I would need to do most likely is ether do a double tap on the breaker or have a splice in the panel. I am sure that double...

Electrical panel [ 2 Answers ]

Please give me details of electrical panels-forms1,2,3 as per british standards

Adding a electrical sub panel [ 1 Answers ]

I am about to add a attached garage with an adjoining workshop. My main pane has no open slots, my question is can I connect to the main wires coming into the panel, and go to a sub panel with a 50amp breaker. If so what size/length wire do I use? Thanks Joel . Email [email protected]


View more questions Search