  • Nov 26, 2007, 10:41 AM
    happyguy
    Double taps at electrical panel
    I have just had a home inspection on my home. The inspector said that I had several double taps. Can these be corrected without adding breakers. The 200 amp panel is almost full.
  • Nov 26, 2007, 10:58 AM
    KISS
    There are three ways that the problem can be corrected:
    1) Add a subpanel
    2) Replace single breakers with tandem breakers
    3) Pigtail the connections

    1) The subpanel requires a large circuit breaker in the main panel. In the sub-panel ground and neutral are isolated. You usually have to purchase a ground bar kit and it will not have a main breaker.

    2) A tandem breaker has two independent circuit breakers in a single slot. There is a label on the panel which specifies the number of "poles" the panel can have. This cannot be exceeded. A "pole" might be defined as the number of places to connect circuits.

    3) Circuits can be pigtailed. A short length of wire connected to the two circuits wirenutted together.
  • Nov 26, 2007, 12:09 PM
    happyguy
    Comment on KISS's post
    Exactly what I needed
  • Nov 26, 2007, 12:22 PM
    labman
    Before adding too many tandem breakers, read the fine print on your box label about how many poles you are allowed.