    Can I butt splice a main breaker ground wire to make it longer
    The ground wire that comes from the meter to the main breaker is too short for the new box I want to install. Can I butt splice the ground to make it longer. This is the 4.0 ground and is about 18" short
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jan 31, 2010, 06:10 PM

    I would use a "Bug".
    This:
    Split Bolt Connectors - Wire Connectors - Electrical - Grainger Industrial Supply
    Hope you mean a #4 ground , not a 4/0 ground.
    airon12's Avatar
    airon12 Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 31, 2010, 06:36 PM
    Quote Originally Posted by Stratmando View Post
    I would use a "Bug".
    This:
    Split Bolt Connectors - Wire Connectors - Electrical - Grainger Industrial Supply
    Hope you mean a #4 ground , not a 4/0 ground.
    It is the ground wire that goes from the 200 amp main outside to the 200 amp main inside I believe it is what they call4/0
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Jan 31, 2010, 06:46 PM

    4/0 is 0000 AWG and about 0.460 in diameter which is a little less than 1/2 inch.
    airon12's Avatar
    airon12 Posts: 4, Reputation: 1
    New Member
     
    #5

    Jan 31, 2010, 07:00 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    4/0 is 0000 AWG and about 0.460 in diameter which is a little less than 1/2 inch.
    That's the one it is the same wire coming from the overhead to the meter socket. I have butt splicer that size and I was told that I could use it to splice the ground but I want to make sure
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Feb 1, 2010, 07:38 AM

    4/0 is a much larger wire than #4,
    You also mention the Ground wire that goes to the Breaker? Are you sure you don't mean the supply wire?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Feb 1, 2010, 07:50 AM
    Probalby is referring to the bare neutral of a 3 wire SE cable.

    This is the grounded conductor, not the "ground".

    The splt bolt method Strat mentioned is fine for this conductor.

    If you have a butt splice for #4/0, you must have the special crimping tool and die?

    A true grounding electrode conductor must be continuous or use a irreversible connection, such as CadWeld, or a compression connector.
    airon12's Avatar
    airon12 Posts: 4, Reputation: 1
    New Member
     
    #8

    Feb 1, 2010, 07:13 PM
    Quote Originally Posted by Stratmando View Post
    4/0 is a much larger wire than #4,
    You also mention the Ground wire that goes to the Breaker? Are you sure you don't mean the supply wire?
    The wire is the ground wire and it 4/0 aluminum I have a butt splicer that size it has burndy ams4/0 on the side of it
    armando1a's Avatar
    armando1a Posts: 2, Reputation: 1
    New Member
     
    #9

    Mar 23, 2010, 11:38 AM
    Are u steel having problem with your ground wire they sala a permanet conector for it and you won't have any problems
    armando1a's Avatar
    armando1a Posts: 2, Reputation: 1
    New Member
     
    #10

    Mar 23, 2010, 11:38 AM
    Are u steel having problem with your ground wire they sala a permanet conector for it and you won't have any problems

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connecting neutral wire to ground wire in breaker panel [ 3 Answers ]

Can the neutral wire be connected to the ground wire at the neutral bar in the breaker panel?

How many feet of wire between main breaker and meter base without a disconnect [ 1 Answers ]

What is the code for the length of wire between the panel box and meter base without installing a disconnect

Re-routing main breaker's ground wire [ 10 Answers ]

Our main breaker is grounded by a wire attached to the main copper water pipe. I need to disconnect this wire from the water pipe, then re-route it to go through Ceiling joist, then reconnect. Question: Is there any danger in this if I shut the main breaker power?

No ground rod at main breaker. [ 10 Answers ]

I have been reading threads here but want to be sure I understand since electricity is potentially so dangerous. I have an old house. My main breaker box below the meter has two large hot legs and an uninsulated neutral. There is no ground terminal. There is no ground rod. I'm sure something is...

Wire sizes and breaker boxes on main lines [ 1 Answers ]

I am currently adding an addition on to my 100 year old house (which has 50 year old wiring). I only have 100 amp service, but this is enough for now. Here is my plan: From the pole to the addition will be a 100 foot stretch of 4/0 cable. I realize that with 100 amp service I do not need that...


View more questions Search