    Can I butt splice a main breaker ground wire to make it longer
    The ground wire that comes from the meter to the main breaker is too short for the new box I want to install. Can I butt splice the ground to make it longer. This is the 4.0 ground and is about 18" short
  • Jan 31, 2010, 06:10 PM
    Stratmando

    I would use a "Bug".
    This:
    Split Bolt Connectors - Wire Connectors - Electrical - Grainger Industrial Supply
    Hope you mean a #4 ground , not a 4/0 ground.
  • Jan 31, 2010, 06:36 PM
    airon12
    Quote:

    Originally Posted by Stratmando View Post
    I would use a "Bug".
    This:
    Split Bolt Connectors - Wire Connectors - Electrical - Grainger Industrial Supply
    Hope you mean a #4 ground , not a 4/0 ground.

    It is the ground wire that goes from the 200 amp main outside to the 200 amp main inside I believe it is what they call4/0
  • Jan 31, 2010, 06:46 PM
    KISS

    4/0 is 0000 AWG and about 0.460 in diameter which is a little less than 1/2 inch.
  • Jan 31, 2010, 07:00 PM
    airon12
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    4/0 is 0000 AWG and about 0.460 in diameter which is a little less than 1/2 inch.

    That's the one it is the same wire coming from the overhead to the meter socket. I have butt splicer that size and I was told that I could use it to splice the ground but I want to make sure
  • Feb 1, 2010, 07:38 AM
    Stratmando

    4/0 is a much larger wire than #4,
    You also mention the Ground wire that goes to the Breaker? Are you sure you don't mean the supply wire?
  • Feb 1, 2010, 07:50 AM
    tkrussell
    Probalby is referring to the bare neutral of a 3 wire SE cable.

    This is the grounded conductor, not the "ground".

    The splt bolt method Strat mentioned is fine for this conductor.

    If you have a butt splice for #4/0, you must have the special crimping tool and die?

    A true grounding electrode conductor must be continuous or use a irreversible connection, such as CadWeld, or a compression connector.
  • Feb 1, 2010, 07:13 PM
    airon12
    Quote:

    Originally Posted by Stratmando View Post
    4/0 is a much larger wire than #4,
    You also mention the Ground wire that goes to the Breaker? Are you sure you don't mean the supply wire?

    The wire is the ground wire and it 4/0 aluminum I have a butt splicer that size it has burndy ams4/0 on the side of it
  • Mar 23, 2010, 11:38 AM
    armando1a
    Are u steel having problem with your ground wire they sala a permanet conector for it and you won't have any problems
  • Mar 23, 2010, 11:38 AM
    armando1a
    Are u steel having problem with your ground wire they sala a permanet conector for it and you won't have any problems