    How many conductors is to many
    I have a 2 gang plastic nail on box with 2 14/3 and 3 14/2 will I get away with that on a inspection
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    Jan 26, 2008, 01:18 PM
    What size is the box (It should say inside)?

    Then get back to us for a calculation
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Jan 26, 2008, 06:47 PM
    Look inside the box. Some have max conductors marked on the inside back. A 2 gang box should allow more than 5 14 conductors
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 26, 2008, 08:25 PM
    One thing, once you find the max amount of conductors stamped inside plastic boxes, you must deduct two conductors for each device to arrive at the net max amount allowed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sizing parallel conductors [ 2 Answers ]

On a 400 amp service for a commercial building. I'm trying to figure out the conductor size using parallel runs. I think 3/0 is sufficient but not sure. 3/0 is good for 225amps under the 90 degree column. Do you then multiply by 2 for 450 amps?

Electrical panel conductors [ 2 Answers ]

What size copper conductors do I need for a 200 amp panel approximetly 150' form the pole. Thank You, Brian

Service Entrance Conductors [ 1 Answers ]

I am currently installing a Single Phase 240 volt 200 amp 3wire service on a residential Home. The breaker box will be located approximately 100' from the utility meter. The copper wire will be ran underground 2'. What size wire will I need to run without having more than a 3% Voltage Drop?

How do I size parallel Conductors? [ 1 Answers ]

I'm curious how to size a service using parallel feeders. If I had a 600 amp, 3-ph service would I simply add together the ampacity ratings of a selected copper wire size or do I need to derate the wire size due to parallel use? Please tell me what size copper I would need to use. I'm assuming I...

Diamonds as electrical conductors [ 2 Answers ]

Will a diamond conduct electricity and, if so, how good a conductor is it?


View more questions Search