    Sizing parallel conductors
    On a 400 amp service for a commercial building. I'm trying to figure out the conductor size using parallel runs. I think 3/0 is sufficient but not sure. 3/0 is good for 225amps under the 90 degree column. Do you then multiply by 2 for 450 amps?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 18, 2007, 06:15 PM
    #3/0 is correct but not because of the 90 Deg C column, but it is rated 200 amps in the 75 Deg C column. Cannot use 90 D column unless the terminals are rated 90 D.

    So parallel #3/0 will be rated 400 amps.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #3

    Oct 18, 2007, 07:14 PM
    Seeing that you said 225A in the begin, we can assume you are using copper:)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire sizing and conduit sizing [ 8 Answers ]

I am looking for confirmation on some of the info I have found and answers to a few missing pieces. This is regarding wire size and conduit size for service conductors from the meter to the breaker panel (about 30 ft away). Wire Size: 125A service needs #2 copper or 1/0 aluminum -- #6 copper...

Electrical panel conductors [ 2 Answers ]

What size copper conductors do I need for a 200 amp panel approximetly 150' form the pole. Thank You, Brian

Service Entrance Conductors [ 1 Answers ]

I am currently installing a Single Phase 240 volt 200 amp 3wire service on a residential Home. The breaker box will be located approximately 100' from the utility meter. The copper wire will be ran underground 2'. What size wire will I need to run without having more than a 3% Voltage Drop?

How do I size parallel Conductors? [ 1 Answers ]

I'm curious how to size a service using parallel feeders. If I had a 600 amp, 3-ph service would I simply add together the ampacity ratings of a selected copper wire size or do I need to derate the wire size due to parallel use? Please tell me what size copper I would need to use. I'm assuming I...

Diamonds as electrical conductors [ 2 Answers ]

Will a diamond conduct electricity and, if so, how good a conductor is it?


View more questions Search