    Service Entrance Conductors
    I am currently installing a Single Phase 240 volt 200 amp 3wire service on a residential
    Home. The breaker box will be located approximately 100' from the utility meter. The copper wire will be ran underground 2'. What size wire will I need to run without having more than a 3% Voltage Drop?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 29, 2007, 02:41 AM
    3% of 240 volts is 7.2 volts dropped. #2/0 copper wire will give 3 volts dropped if the service is loaded to 80%.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable [ 23 Answers ]

I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...

Service entrance cable [ 2 Answers ]

Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire

Modifiying service entrance [ 1 Answers ]

I am in the process of building a new addition and attached garage. I currently have 200 amp service 4/0 alum. 100 feet UG from house to (my) pole in 2" conduit. It then crosses the street to utility owned pole, approximately 125 feet OH. (dashed yellow line) I would like to remove the...

Al service conductors... Special Procedures? [ 2 Answers ]

Hi all. I hope you can point me in the right direction. I have seen two references in books to special procedures with Al service conductors. I'm installing 4/0 AL for a 200A service. I understand you have to retourque the terminations a day after installing, and that it's good to use an...

Service entrance [ 5 Answers ]

Can someone tell me how to find out what the amp rating of a service to a house is . The fuse box is old with edison base fuses, but the weather head and pipe to the meter cradel looks newer want to change to beaker panel Not sure what size


View more questions Search