    I have a junction box with 3 circuits passing through it…
    Should all the neutral s be connected?
    The circuits are 2-15amp and a 20 amp
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 8, 2007, 12:22 PM
    No, do not connect all the neutrals from several circuits together. Each neutral needs to be pared up with it's respective hot thruout the entire circuit. The neutrals should only join together at the neutral bar in the breaker panel.
    ebaines's Avatar
    ebaines Posts: 12,131, Reputation: 1307
    Expert
     
    #3

    Aug 9, 2007, 08:08 AM
    Agree with tkrussell - but to be clear the grounds should have course all be tied together and to the box.
    MOWERMAN2468's Avatar
    MOWERMAN2468 Posts: 3,214, Reputation: 243
    Ultra Member
     
    #4

    Aug 9, 2007, 08:33 AM
    Be Certain To Ground The Box When You Tie All The Ground Wires Together.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Aug 10, 2007, 07:27 PM
    If you need to separate, need to make sure 2 circuits sharing same neutral. Are on opposite phases.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Outdoor junction box [ 2 Answers ]

The house I bought has an GFI outlet in the middle of the back yard (they had a pool). I want to remove that outlet and place it further at the back of the property. Is there a issue with splicing the old wires to new ones w/wire nuts, putting them in a small junction box & burring it?

Electric junction box [ 1 Answers ]

How do you wire a 220 volt line through a junction box into a 220 volt plug in for a stove? Please provode me with a schematic of the wiring procedure. Thanks

Junction box as a cover? [ 3 Answers ]

I have a junction box currently that I need to add wiring to. It has the opening and internal clamps to add two more wires but this would put the box over its legal limit of wires in the box. The box is in a location that can be gotten at without removing any part of the building. The box is...

Junction Box Fill [ 5 Answers ]

I'm trying to find what the fill capacity on electrical junction boxes are. I found this chart The thing that is stumping me is do you count grounds or not? For example, the specific instance that has me looking is that I have a 4x4x1 1/4 box, with 4 12/2 cables in it. If you don't...

Junction Box size [ 2 Answers ]

I have and oven with 10/3 mc cable attached. I am going to splice this to a 10/3 romex cable that I pulled from the sub panel. Is a metal 3" deep single gang box big enough? How many cubic inches do I need? Thank you


View more questions Search