    Bryant code 13
    Hi,
    Woke thismorning to a cold house and a blank thermostat. After some investigation , found the 24vac at the thermostat and the furnace terminal to be dead. Reset the breaker and the furnace tried to fire. Blower ran, inducer ran igniter lit and burners ran for about 5 sec and shut down. Flashed code 33 after a few tries it began to flash 13. Little more investigation into code 33 led me to find the condensate trap pluged and drained about 1/2gallon of water from the system. Cleaned all hoses and cleared the blockeage and its been running fine since. The question I have is will the lockout code13 cause the loss of the 24vac to be shut down to tbe thermostat circuit or do I have another intermittent issue?
    Bryant plus 90i 12yrs old
    Blower replaced in 06
    Inducer in08
    Heat exchanger in 08
    Heat e changer was pluged no doubt caused by the blocked condensate trap. The debris cleared from the trap looked just like the stuff blocking the origonal heat exchanger.
    Note: unit running on propane.
    Any thoughts?
    Thanks
    Jeff.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Oct 19, 2013, 04:34 PM
    Have someone come in, flush the heat exchanger, & set up the furnace with combustion test instruments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant plus 90 code 31? [ 0 Answers ]

Having a similar problem. Just started this heating season. After several times of "fixing" it without really knowing what I did, the last time I happened to bump the pressure switch while it was running and the burners went out (I am thinking the pressure switch has to stay activated while unit...

Plus 90 bryant code 23 [ 0 Answers ]

I disconnected one wire to the pressure switch, reconnected it and the draft inducer started and all was well, for overnight... same problem and solution in the AM.. do I need to replace the pressure switch?

Bryant code 33 [ 0 Answers ]

Hi, I really hope someone can help me. I have a Bryant 340MAV. I cannot seem to get the furnace to stop flashing code 33. It doesn't go to 13 either, which I find strange. I also tried bypassing the limit switch, temporarily, just to see if this was the problem. Still getting 33. Also...

Bryant Plus 80 code 14 [ 0 Answers ]

I have a bryand plus 80 heater. It will work some of the time but the other times it will try to start and then stop and flash code 14... ignition lockout. What would be causing this.

Bryant code 42 [ 1 Answers ]

When the furnace is given the self test all appear to run fine the inducer hi and low, blower high and low and igniter glows. Furnace shuts down after about 2 min on high output. Could it be the control board?


View more questions Search