  • Oct 19, 2013, 02:21 PM
    jjnew
    Bryant code 13
    Hi,
    Woke thismorning to a cold house and a blank thermostat. After some investigation , found the 24vac at the thermostat and the furnace terminal to be dead. Reset the breaker and the furnace tried to fire. Blower ran, inducer ran igniter lit and burners ran for about 5 sec and shut down. Flashed code 33 after a few tries it began to flash 13. Little more investigation into code 33 led me to find the condensate trap pluged and drained about 1/2gallon of water from the system. Cleaned all hoses and cleared the blockeage and its been running fine since. The question I have is will the lockout code13 cause the loss of the 24vac to be shut down to tbe thermostat circuit or do I have another intermittent issue?
    Bryant plus 90i 12yrs old
    Blower replaced in 06
    Inducer in08
    Heat exchanger in 08
    Heat e changer was pluged no doubt caused by the blocked condensate trap. The debris cleared from the trap looked just like the stuff blocking the origonal heat exchanger.
    Note: unit running on propane.
    Any thoughts?
    Thanks
    Jeff.
  • Oct 19, 2013, 04:34 PM
    Grady White
    Have someone come in, flush the heat exchanger, & set up the furnace with combustion test instruments.