    Challenger 200amp panel
    I have a 1993 challenger 200amp panel. This panel is in my shop and has 8 ft fluorescent light that are on 15 amp breakers. 3 sets per breaker. All the neutral wires have melted insulation on them 2 inches out from the Neutral buss bar. Could you please tell me why this would happen. Every thing on the other side bar is OK...
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #2

    Jan 1, 2013, 09:10 PM
    If it were only one wire with melted insulation I would suspect a loose connection; but if it's every wire on the bar, I have no idea. Have you had any unusual things going on electrically in your shop lately?

    Someone else here will probably provide a better answer, in the mean time, I would shut off power to the panel.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Jan 2, 2013, 10:00 AM
    ... are you sharing neutrals on these circuits?
    Are the ballasts all magnetic or electronic?
    What size were the neutral conductors?

    Aside from the above questions, I would strongly recommend measuring the neutral current on all the neutrals after you repair them... non-linear loads and poorly connected neutral sharing circuits can contribute to overload conditions on the neutral conductors...
    Don't guess at this... put an amprobe on the neutrals and let us know!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jan 2, 2013, 10:04 AM
    I suspect only one wire was loose and the heat migrated to the other conductors.

    Cut off the burnt portion of each conductor to get to clean copper.

    You should replace this neutral bar, unless there are clean wire ports to use. Do not use the same holes the burnt wires were in.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200amp to sub-panel with SW 4/0 or SM 4/0 [ 3 Answers ]

Hi I have a 200 amp Federal Pioneer main panel and a 60amp going to my sub-panel in a detached garage 93 feet away. I have purchase a 105,000 BTU Pool Heater so I think that I need to change the cable going to the sub-panel. I have a person that has 3 rolls of 125' of SW 4/0 for sale. In...

200amp main panel with 200amp sub panel [ 6 Answers ]

Hi - I'm in Colorado and about to do an electrical service panel upgrade along with a sub panel install. (I should note here that I am an electrician - Australian, so the rules I'm used to are different here in the US). I've applied for and received the relevant permit from the city, but...

Can I upgrade my panel to 200amp from 100amp [ 3 Answers ]

My utility company feeders are 1/0 aluminum... can I upgrade from 100amp panel to 200 amp panel with the existing feeders or do I need to call them?

Challenger SB20 Disconnect Panel Replacement? [ 1 Answers ]

Hello all... I am new on this message board. I have a hopefully simple question. I need to replace the buss bar unit in my Challenger SB20 (200 amp) home disconnect panel. I have searched for individual parts, complete panels and have found nothing. Is this company STILL in business? Does anyone...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...


View more questions Search