    200amp main panel with 200amp sub panel
    Hi -

    I'm in Colorado and about to do an electrical service panel upgrade along with a sub panel install. (I should note here that I am an electrician - Australian, so the rules I'm used to are different here in the US).

    I've applied for and received the relevant permit from the city, but want to make sure I get everything done properly first time so as to not waste the inspector's time and such.

    1. I'll be replacing the current 100 amp service panel with a new 200 amp service panel. Was planning to use a GE brand panel. No problems there?

    2. I want to install a separate 200 amp sub panel in my workshop to run wood working equipment. Can I install a set of 100amp breakers in the main panel to run to the sub panel, thus giving me the 200 amp at the sub panel?

    Thanks Robert
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 30, 2009, 11:50 AM
    My answers follow your questions:

    1. I'll be replacing the current 100 amp service panel with a new 200 amp service panel. Was planning to use a GE brand panel. No problems there?

    GE is a widely popular product. No problems.


    2. I want to install a separate 200 amp sub panel in my workshop to run wood working equipment. Can I install a set of 100amp breakers in the main panel to run to the sub panel, thus giving me the 200 amp at the sub panel?

    Please explain this. A set of 100 amp breakers to get 200 amp? You need a 200 amp breaker to protect a 2oo amp panel.
    youngfield's Avatar
    youngfield Posts: 6, Reputation: 1
    New Member
     
    #3

    Oct 30, 2009, 11:54 AM
    Hi tkrussell

    Sorry - goof on my part - I meant to write.. "200amp breakers in the main panel to run to the sub panel, thus giving me the 200amp at the sub panel". I should have re-read my original post. Sorry.

    So... 200amp main panel with 200amp breakers feeding panel, and a set of 200amp breakers in the main panel feeding to the sub panel. Would that be acceptable for code? Thanks

    Robert
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 30, 2009, 02:33 PM
    Need a 2 pole 200 amp breaker as the main. You can use another 200 amp brekaer to feed a sub. Keep in mind, the service entracne will be a three wire, and after the main the feeder will be a 4 wire.
    youngfield's Avatar
    youngfield Posts: 6, Reputation: 1
    New Member
     
    #5

    Oct 30, 2009, 02:36 PM
    Thanks tkrussell - I think you've answered my questions very nicely. Appreciate your help.

    I hope I understand the three wire main (2 x hots and neutral) and the four wire feed (2 x hots, neutral and ground).

    Robert.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Oct 30, 2009, 05:20 PM

    Problem is, you may no be able to find a 200 A breaker for the panel. You may be limited to 100 or 125 A max.

    Nonetheless, you can still use a 200 A main breaker sub-panel fed with 100-125 A. The wire would be sized for based on the feeding breaker.

    You keep the neutrals separate in the sub. Remove the grond bonding screw ans purchase a ground lug kit when main breaker panels are used as subs.

    A ground rod is required if he structure is detached.
    youngfield's Avatar
    youngfield Posts: 6, Reputation: 1
    New Member
     
    #7

    Nov 2, 2009, 03:41 PM
    Yep - I think it is going to be hard to get a 200amp to feed the sub - so I'm going to use a 125A and a 125A sub. Don't really need 200 at the sub.

    Thanks guys.
    -

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I upgrade my panel to 200amp from 100amp [ 3 Answers ]

My utility company feeders are 1/0 aluminum... can I upgrade from 100amp panel to 200 amp panel with the existing feeders or do I need to call them?

Install 200amp subpanel from 400amp main panel [ 8 Answers ]

Building a new home. The detached garage has a 400amp service panel which is hardly used (has 2 20amp breakers for garage lights). I want to install a 200amp panel in the house basement which is located about 100 feet from the garage panel. I have purchased and installed the 200amp panel in...

Wiring of a 200AMP main panel - SEU wires entry point [ 3 Answers ]

Hello, I am putting a new 200AMP main panel in a service upgrade. Its location is a little higher than the meter socket. The panel and the meter are back to back on a wall (meter outside, panel inside). Main disconnect is at the top of the panel, as are the connections for the SEU cable. Can I...

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

Might scrap 200amp upgrade and go with a bigger 100amp panel [ 10 Answers ]

Hey all! Reading all the posts about 200amp panels and the costs is making my head hurt along with my wallet. I think I will just have the existing 100 swapped out for a larger panel... say a 30/30 100amp (or are there larger ones? ). I live in a 77+ year old house with some older knob&tube...


View more questions Search