Ask Experts Questions for FREE Help !
Ask
    GabrielB's Avatar
    GabrielB Posts: 2, Reputation: 1
    New Member
     
    #1

    Dec 21, 2009, 08:59 PM
    One thermostat for two baseboard heaters wired this way
    Hi guys,


    I have been upgrading my thermostats here in the house and I have a little challenge now.

    Two baseboard heaters that I assume are wired parallel (you will be able to confirm) had their own unit mounted thermostat. I'd like to upgrade as well but for those two I'd like to use the same thermostat to control them. (same room)

    Those 240V baseboards are wired to a 15A breaker with #14 wires.

    I've included pictures from the two heaters. Heater 2 is fed from heater 1 to its left side. All wires on heater 1 are located on its right side. Heater 1 is fed to its right side from a third baseboard in another room.

    I'm not sure how to connect eveything so the thermostat will control both of them correctly. (thermostat is rated with more than enough watts for the two baseboards.)

    I have found similar questions to mine on the web and even here but it didn't address the specific wiring questions here.

    Thanks for your help!
    Gabriel


    Heater 1




    Heater 2



    Diagram (very rough sketch that I did for myself at first - hope it will do. W=white. B=Black)
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Dec 21, 2009, 09:45 PM

    Confirm a few things:

    Heater #2 looks like it has a thermal protector in series with the heater. I suppose heater #1 has on on the other side?

    The thermostat that your going to use has 4 wires and is a line powered thermostat?

    The existing thermostat isn't pictured. Where does it fit in this picture?

    Where did you plan to get power from?

    You do realize that wiring for baseboards must be oversized by 1.25 because it's a space heating load.

    i.e. if the current was 14 A by dividing watts by 120.. You would have to multiply 14 by 1.25 and get 17.5 amps. This would require 12 AWG wire and a 20 A breaker.

    This is done for space heating loads.

    Where are you getting power from for these heaters?

    What is the wattage of each?

    You can post pics directly to this forum using go advanced/manage attachments.
    GabrielB's Avatar
    GabrielB Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 22, 2009, 10:24 AM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Confirm a few things:

    1) Heater #2 looks like it has a thermal protector in series with the heater. I suppose heater #1 has on on the other side?

    2) The thermostat that your going to use has 4 wires and is a line powered thermostat?

    3) The existing thermostat isn't pictured. Where does it fit in this picture?

    4) Where did you plan to get power from?

    5) You do realize that wiring for baseboards must be oversized by 1.25 because its a space heating load.

    i.e. if the current was 14 A by dividing watts by 120.. You would have to multiply 14 by 1.25 and get 17.5 amps. This would require 12 AWG wire and a 20 A breaker.

    This is done for space heating loads.

    Where are you getting power from for these heaters?

    What is the wattage of each?

    You can post pics directly to this forum using go advanced/manage attachments.
    Hi Keepitsimple

    Just so you know those baseboards have been in use for many years. I'm just upgrading the thermostats. The three baseboards connected to the circuit are 750W, 1000W and 1250W. = 3000W.

    A little short of 80% of the 3600W of the 240V 15A breaker. (2880W)
    But like I said it's always been like that...

    1) Yes. I assume this is what you're talking about?


    2) No. It's a two pole thermostat as are all the other ones in the house, except one.

    3) It's been removed. It was a simple dial like this
    But again, only two wires. Single pole.

    4) What do you mean? Those are already powered. 3 heaters in parallel.

    5) Yes. See above.


    I hope this shed light on the matter.
    What do you suggest?


    Thanks!
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Dec 22, 2009, 11:36 PM

    Sorry I didn't get back to you sooner.

    2) A two pole thermostat would have 4 wires and essentially two switches inside. On switch is turned off on a rise in temperature and the other is turned off when the thermostat is turned to the off position. Just like a 2 pole breaker has two connections to the bus and 2 connections to the load, so would a two pole thermostat.

    The black thing looks like an overtemperature (OT) device, so for all intents and purposes the side with the OT device and all the wires, we will call black to be the black after the OT device.

    The other heater black is black.

    What you want to do is connect the reds together and the blacks together to put the heaters in parallel.

    One way to do that which may already be done is a cable then runs between the two heaters. Proabaly makes sense to connect black of the cable to black of the heaters and white of the cable to red of the heaters.

    Now you have the heaters tied together.

    Pick one of the heaters and run a cable to the thermostat load terminals. Connect to the black and white cable that connects both heaters together. You will have all the blacks tied together and 2 whites and 1 red tied together.

    Connect power to the line input(s) of the thermostat.

    Here is an example single pole and double pole thermostat.

    http://www.luxproproducts.com/pdfs/lv1-2_eng.pdf

    Note the LV-1 (single pole) should be used on 120 V systems and the LV-2 is intended for 240 V systems.

    What I'm getting from you is that your separating the heaters into two heaters and one thermostat and 1 heater and another thermostat.

    As it stands, I think, you have one thermostat connecting to all of the heaters, so the cable that goes from one room to the other needs to be removed since it is controlled by the thermostat in the other room.

    Your picture didn't make a lot of sense. I hope my wording did.

    Somewhere, I think you mentioned that the tstat was on the heater. If that's the case, then you can use the existing wire for power.

    It's customary to run power to the switch and then to the heaters for 240. I hope the tstat is not in a "switch loop" where power runs to the heater first and then two wires run to the thermostat. This would be incorrect for the US.

    Yep, your right 3600/240*1.25=15.625 A which is slightly over 15 A.

    If it's easier, you could just run another wire from the panel for power.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

2 baseboard heaters 1 thermostat [ 9 Answers ]

I am trying to install 2 2500 watt baseboard heaters each on its own 240v 20 amp circuit. That part I can do, but I want to tie them into one thermostat, How is this done? Anyone help,Thanks

Electric Baseboard Heaters and Thermostat [ 4 Answers ]

I have 6 electric 220V heaters powered by two separate 20A circuits. All heaters are wired to a single thermostat. The thermostat is labeled 24V, and only has a small red and white wire running to it (far smaller than 10# or 12# wire.) I would like to replace this thermostat with a progammable. ...

Wiring 2 baseboard heaters to thermostat [ 1 Answers ]

I recently moved in and the thermostat connected to 2- 2000 watt baseboard heaters shorted out. The burnt out thermostat only had 2 wires, a black and white. Was it the wrong kind? Was it for a single baseboard heater? I purchased a double line dimplex thermostat to replace it. I have 240 VAC....

Wiring thermostat and 2 baseboard heaters [ 1 Answers ]

Hey guys can you double check my plan for wiring my two new baseboard heaters 12/2 Romex(blk/white/bare ground) 20 amp Square D QO 240v breaker Honeywell TL8230 Line Pro 800 double pole 240v 3600w 15 amp load 2x Qmark HBB-1504 heaters 240v 6.25amps 1500w 1. Main off 2. install breaker

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...


View more questions Search