    Wiring 2 baseboard heaters to thermostat
    I recently moved in and the thermostat connected to 2- 2000 watt baseboard heaters shorted out. The burnt out thermostat only had 2 wires, a black and white. Was it the wrong kind? Was it for a single baseboard heater? I purchased a double line dimplex thermostat to replace it. I have 240 VAC.
    The wires from the Dimplex thermostat are 2 red and 2 white. Do I connect the 2 Red to the white wire from the wall box and the two Black to the black?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 21, 2008, 03:51 PM
    The unit no doubt came with instructions. They will be your biggest help.

    The t-stat you had was a single pole. Fine for what it was doing.
    To use the new one properly you need to remove the splice in the wall box and un-do it.
    You then need to determine which is the pair of wire that is the LINE.

    Before I go to far with this. What is your level of expertise? Have you worked on this type of thing before? Do you have a decent electrical tester?

    You will be testing for 240 volts. This is nothing to mess around with if you don't know what you are doing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Baseboard Heaters [ 5 Answers ]

I am wiring two Marley electric baseboard heaters (240v) to a Programmable Thermostat and want to confirm the layout. BASEBOARDS Both Baseboards are 8 feet long, 240 volt, 2000 watt, 8.3 amps WIRE & Circuit BREAKER I am using 12/2 wire and connected to a double pull 20 amp circuit...

Wiring 240 electric baseboard heaters with 2 pole thermostat. PROBLEMS ENCOUNTERED. [ 5 Answers ]

Howdy all, I have looked at the previous postings as I frequent the site for help on subjects. I am however perplexed as to what I have done wrong. I am installing 4 electric heaters, on 2 separate 240 breakers. Each breaker is 30 AMP. I used 12/2 Red Heat resistant wire and ran the line...

Wiring thermostat and 2 baseboard heaters [ 1 Answers ]

Hey guys can you double check my plan for wiring my two new baseboard heaters 12/2 Romex(blk/white/bare ground) 20 amp Square D QO 240v breaker Honeywell TL8230 Line Pro 800 double pole 240v 3600w 15 amp load 2x Qmark HBB-1504 heaters 240v 6.25amps 1500w 1. Main off 2. install breaker

Wiring wall mounted thermostat-operating two baseboard heaters [ 7 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I will be using one 240 V 2 wire circuit running two heaters at a total of 3800 watts. I would like to have both heaters controlled by one wall mounted double pole thermostat. How do I run the...

Electric baseboard heaters -wiring 1 thermostat to two heaters [ 2 Answers ]

I would like to heat my new garage with electric baseboard heaters. The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire. I would like to have both heaters controlled...


View more questions Search