2 baseboard heaters 1 thermostat
I am trying to install 2 2500 watt baseboard heaters each on its own 240v 20 amp circuit. That part I can do, but I want to tie them into one thermostat, How is this done? Anyone help,Thanks
|
|
 |
Ultra Member
|
|
Mar 22, 2009, 03:47 PM
|
|
Separate circuits will probably require separate thermostats, unless you incorporate some type of relay to isolate the heater circuits from the thermostat.
|
|
 |
New Member
|
|
Mar 22, 2009, 05:09 PM
|
|
Do they not make a thermostate that can handle two circuits?
|
|
 |
Plumbing Expert
|
|
Mar 22, 2009, 05:17 PM
|
|
No, not that I've ever seen.
|
|
 |
Ultra Member
|
|
Mar 22, 2009, 05:27 PM
|
|
Some line voltage thermostats for applications like yours do have 2 circuits, but they are intended to break both lines to the heater. The contacts won't last long if used to break one line to each heater.
|
|
 |
New Member
|
|
Mar 22, 2009, 08:21 PM
|
|
It seems to me that this problem must have been encountered before I am surprised that there is no apparent solution? Not sure what to do!
|
|
 |
Ultra Member
|
|
Mar 22, 2009, 08:43 PM
|
|
Is there some reason that you cannot install separate thermostats for each heater?
|
|
 |
Uber Member
|
|
Mar 22, 2009, 10:06 PM
|
|
Well, if you really want to, but don't want to run a lot of wires, but to tell you the truth, you can use an HVAC tstat and two 24 VAC contactors and your done. That may allow other options.
You need 20.83 Amps for both heaters together. A line voltage stat that can handle that should be findable. Just connect the heaters in parallel.
Since these are space heating, the wiring need to be sized to 125% of total load.
You can also, use a current switch and a contactor, if you want them to be separate and use a line stat. You feed one of the conductors around the sensor and use the pilot duty relay to energize a contactor for the other one.
There are all sorts of ways. Each will have different costs and capabilities.
|
|
 |
New Member
|
|
Mar 23, 2009, 08:23 AM
|
|
Both heaters are in the same room, It doesn't make sense to have 2 thermostates
|
|
 |
Uber Member
|
|
Mar 23, 2009, 11:23 AM
|
|
Hey KC13:
In a new building that was moved to in the early 90's. Air to water heat pumps everywhere. One room had two heatpumps because of an unusual load.
Two thermostats, both auto-changeover. Talk about innefficient.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Electric Baseboard Heaters and Thermostat
[ 4 Answers ]
I have 6 electric 220V heaters powered by two separate 20A circuits. All heaters are wired to a single thermostat. The thermostat is labeled 24V, and only has a small red and white wire running to it (far smaller than 10# or 12# wire.) I would like to replace this thermostat with a progammable. ...
Baseboard heaters not heating to thermostat temperature
[ 2 Answers ]
It won't let me ask question in heating and air conditioning. It keeps referring me to register or login which I did but it still won't do anything when I click on ask button. I need help with electric baseboard heater. It is 59 degrees in my house and temp is set to 69. It is -8 outside. We...
Wiring 2 baseboard heaters to thermostat
[ 1 Answers ]
I recently moved in and the thermostat connected to 2- 2000 watt baseboard heaters shorted out. The burnt out thermostat only had 2 wires, a black and white. Was it the wrong kind? Was it for a single baseboard heater? I purchased a double line dimplex thermostat to replace it. I have 240 VAC....
Wiring thermostat and 2 baseboard heaters
[ 1 Answers ]
Hey guys can you double check my plan for wiring my two new baseboard heaters
12/2 Romex(blk/white/bare ground)
20 amp Square D QO 240v breaker
Honeywell TL8230 Line Pro 800 double pole 240v 3600w 15 amp load
2x Qmark HBB-1504 heaters 240v 6.25amps 1500w
1. Main off
2. install breaker
Electric baseboard heaters -wiring 1 thermostat to two heaters
[ 2 Answers ]
I would like to heat my new garage with electric baseboard heaters.
The new garage is 20X24 feet. I would like to use only one 240V #12 2 wire circuit running two heaters at a total of 3800 watts. I plan to use 2 pole 20A breakers and 2c #12 wire.
I would like to have both heaters controlled...
View more questions
Search
|