    3PH 480V motor wiring and tripping on overload
    :confused:REPLACED EXISTING DAYTON MOTOR WITH EXACT MODEL NUMBER. 3PH 480V
    WIRED IT EXACTLY AS SHOWN ON NAME PLATE. KEEP TRIPPNG BREAKER. NAME PLATE INDICATES 1.9AMP FULL LOAD. I MEASURE 3.4AMP. MOTOR IS USED FOR BELT DRIVEN
    BLOWER. IREMOVE BELT AND I HAVE 1.4AMP READING IS THIS NORMAL(NO LOAD) READING
    .
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    May 15, 2009, 11:15 PM
    Check all 3 legs of the circuit for exact voltage readings. Low voltage on one or more legs will cause the problem you are having.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    May 16, 2009, 04:40 AM

    Could be possible that rotation is incorrect. This would cause the FLA to increase beyond the nameplate FLA, and cause the overload to trip.

    If so, just swap any two leads of the 3 phase wiring.

    Or the pulley or fan that the belt is driving could be stiff, bound, or otherwise too tight, bad bearing, for example, which would cause the FLA to be too high.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    May 16, 2009, 05:19 AM
    On a belt driven blower a reverse rotation will cause less of a load since it will not be moving the air since the wheel will not be scooping up the air. Now a adjustable pully can cause problems if not adjusted properly.
    jerro's Avatar
    jerro Posts: 172, Reputation: 5
    Junior Member
     
    #5

    May 16, 2009, 06:17 AM

    Are you tripping the main breaker for the ac unit or tripping the overlaod heaters. This makes a difference as to what to look for. What was the reason for changing the motor?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a AOS fan motor [ 1 Answers ]

I replaced my old fan motor with a AOS fan motor with white,black,brown,brown w/white stripes where do they go? My Previous fan motor had yellow and brown wire-nut together,purple,orange and black wires.

Motor wiring [ 3 Answers ]

I have replace a seized up motor this weekend. Motor would not run. Talked to a HVAC man who lives far away, explained the board is shot. Today I replaced the rodgers-white circuit board. Need help in connecting the motor wires. The two brown are connected to the capacitor. Black...

Fan motor wiring [ 2 Answers ]

The model is Carrier 42JS012. Can anyone tell the air-cond fan motor wiring? The are 5 wires which is Red, Yellow, Blue, Black and White. Which wire is connected to the capacitor and which is connected to fan speed? Thanks

Motor wiring? [ 2 Answers ]

I have a new GE commercial motor model # 5KC35JNA489Y, 115v to replace the one on a metal lathe. It has 5 wires, purple, blue, black, white and yellow.. there is a separate switch for forward and reverse.. I'm not sure how to wire this.. any help would be very appreciated

Motor wiring? [ 4 Answers ]

:mad: Perhaps someone here can help me, I bought a small GE 120v electric motor for a replacement for a machine. It has 3 three wires (red, yellow,blue) and requires a 10mf capacitor. My best guess was to wire it with Blue to line , red-line & cap, and yellow on the other cap term. But it runs very...


View more questions Search