    Can you use a 15 amp receptacle on 20 amp breaker
    Can you use 15 amp outlet plug on a 20 amp breaker
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #2

    Nov 17, 2008, 09:59 PM
    Quote Originally Posted by dilln12 View Post
    can you use 15 amp outlet plug on a 20 amp breaker
    A receptacle with a 15 or 20 amp rating can be installed on a 20A circuit.

    If the receptacle is rated for 15amps only, then no.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 18, 2008, 05:05 AM
    If it is a duplex receptacle then yes, you can install a 15A receptacle on a 20A circuit.
    A 15A simplex (single) receptacles cannot be on a 20A circuit.

    This does not apply to Canada.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Circuit Breaker/Wiring/Receptacle Ratings [ 3 Answers ]

If you run from a 20 amp breaker with 12/2 wire each receptacle rating has to be 20 amps? 20amp breaker-------->with 12/2 wire------->to 5 outlets In other words if you go to the store to buy the receptacles they can't say on them 15A max because the breaker it is run from is a 20 amp right?...

Adding a 20amp receptacle to a 15amp breaker [ 2 Answers ]

Hi All, I need to install a small tankless water heater (made for under the lavatory sink) for the sink in my bathroom. The specs on the water heater are: 120 Volts, 2.4kW, 20 Amps, wire size: 10AWG. My question is this... The existing bathroom outlet that I want to splice into to add this water...

New 15A breaker trips main 100A breaker [ 6 Answers ]

Hi, I've been finishing my basement and I added a few 15A breakers One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets. When installing the drywall I accidentally shorted the outlet closest to the panel. It...

GFCI Breaker vs Receptacle [ 1 Answers ]

I'm adding some 20A circuits in my garage/shop and know that they have to be GFCI protected. My question is this: Is there an advantage to using a GFCI breaker over just putting a GFCI receptacle in the first slot of the series? Thanks.


View more questions Search