Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Can you use a 15 amp receptacle on 20 amp breaker (https://www.askmehelpdesk.com/showthread.php?t=282180)

  • Nov 17, 2008, 09:30 PM
    dilln12
    Can you use a 15 amp receptacle on 20 amp breaker
    Can you use 15 amp outlet plug on a 20 amp breaker
  • Nov 17, 2008, 09:59 PM
    Washington1
    Quote:

    Originally Posted by dilln12 View Post
    can you use 15 amp outlet plug on a 20 amp breaker

    A receptacle with a 15 or 20 amp rating can be installed on a 20A circuit.

    If the receptacle is rated for 15amps only, then no.
  • Nov 18, 2008, 05:05 AM
    stanfortyman
    If it is a duplex receptacle then yes, you can install a 15A receptacle on a 20A circuit.
    A 15A simplex (single) receptacles cannot be on a 20A circuit.

    This does not apply to Canada.

  • All times are GMT -7. The time now is 03:09 PM.