New Member
|
|
Feb 14, 2007, 07:08 AM
|
|
New 15A breaker trips main 100A breaker
Hi,
I've been finishing my basement and I added a few 15A breakers
One room has 8 outlets in series with the first starting about 6 feet from the main panel. There is currently no load on this outlets.
When installing the drywall I accidentally shorted the outlet closest to the panel. It tripped the breaker, but it also tripped the main breaker. The wiring is 14/2.
I don't think this is normal. Is the breaker bad? Are there other things I should look for?
|
|
 |
Home Repair & Remodeling Expert
|
|
Feb 14, 2007, 08:47 AM
|
|
It does sound like your 15a breaker is bad or wired improperly. Shut off the main and check the 15a for continuity both open and closed. I usually don't mess with a breaker that may be bad, replacement is not very expensive so I go that route.
|
|
 |
Uber Member
|
|
Feb 14, 2007, 08:53 AM
|
|
It sounds to me like the new breaker didn't do its job, but the main did. Wonder if you got ahold of a bad batch? I would wait and see what tkrussel has to say.
I am glad people now have him for these tough questions.
|
|
 |
Uber Member
|
|
Feb 14, 2007, 09:06 AM
|
|
No, most likely neither breaker is defective. What you saw was the effect of what is called "AIC" or Available Interrupting Current, and low impedance of the circuitry and the grounding. Other than the nusinance tripping of the Main, all of this is a good thing.
Having a dead short so close to a panel results in the low impedance (AC resistance),causing the short circuit current to rise very high very quickly, which was above the threshold of the Main to cause it to trip in additon to the branch circuit breaker.
This is normal is those rare situations where several factors are "just right" so to speak.
I would not worry about anything at the moment, however, if the Main does trip too easily in the future, it may be an indication of being weakened, and will need to be replaced.
If for some reason you are not comfortable with my explanation or the condition of the main breaker, may be worth replacing anyway for the $40.00 and peace of mind.
|
|
 |
New Member
|
|
Feb 14, 2007, 09:34 AM
|
|
Thanks for the advice.
The house is new so the main breaker should be in good condition, but it tripping just got me a little worried. When this happened I double checked the connections in the main panel and even tried swapping breakers (I bought 2) and both had tripped the main (and theirs) from shorting the first outlet.
Should I try to trip the breaker from farther down the circuit, e.g.. The last connect outlet? I did not want to do this more as I read that it is not good for the wiring.
|
|
 |
Uber Member
|
|
Feb 14, 2007, 11:11 AM
|
|
First of all I have to assume the short is now cleared and the damaged cable has been replaced.
No need to test the breakers by intentionally shorting anything. Leave well enough alone, being new makes me feel better.
I did not get into a complete explanation of AIC rating, this is fairly complex topic not for this forum, but part of the cause of the main tripping, again nothing to worry about.
If you like to do more research do a Google search for AIC, fault current, short circuit current, there are other terms that all mean the same thing, but this enough to get started.
|
|
 |
Uber Member
|
|
May 19, 2007, 12:56 PM
|
|
I have seen shorts, Very solid and direct trip 2 breakers, Replace if you have the money, it's probably OK. Worse I have seen by not replacing, is lower amp trip.
I would tighten every Breaker, Lug, Neutral and Ground. Especially Main Breaker.
Any further problem, change Main. 15 may be OK.
If replacing will make you sleep better, Small price for sleep.
|
|
Question Tools |
Search this Question |
|
|
Check out some similar questions!
Oven trips breaker
[ 1 Answers ]
I am having tile put down and the tile guy moved the stove to tile under it. I used the stove yesterday morning. He tiled under the stove and put it back - unplugged. I went to plug it in this morning and it keeps tripping the circuit breaker. I unplugged the stove and flipped the breaker and...
#00 to 100a breaker
[ 1 Answers ]
A friend of mine ran #00/3 from his house to his garage, but only wants a 100a service. What can I use to hook up #00 to a 100a main breaker, because I don't think the physical size of the wire will fit under the lugs in the breaker. Also I plan to run a #6 to a ground plate buried 3' outside the...
Breaker Trips
[ 3 Answers ]
My furance Circuit breaker The main from the house input has stated to trip. It has happened twice this past weekend?
Any ideas?
View more questions
Search
|