    Shared neutrals - two circuits on 12/3 romex
    I want to run two circuit with 12/3 Romex. Circuit #1 will be 3 light fixtures and circuit #2 will be two GFCI Receptacles. I am concerned about having shared neutral. From reading other post it is advised to splice all neutral and not use screw terminal to connect the two circuits. Also I will not be using the load side of the GFCI receptacles.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2007, 01:50 AM
    Shared neutrals are fine, still very popular in homes, thou a loose connection can cause some problems. Splicing at a device and not using screw terminals is not just wise advice, it is also required by code.

    Just be sure any splices up to the point the two circuits split off are good and tight, along with the connections in the panel, and you will not have any problems.
    lwchris's Avatar
    lwchris Posts: 16, Reputation: 1
    New Member
     
    #3

    Jun 9, 2007, 05:40 PM
    Should I used a Double Pole Breaker. So that if one side of the breaker trips the other side will as well? Also is this OK in a commercial environment?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Jun 9, 2007, 06:05 PM
    It can be on 2 single pole breakers.
    Unless it is in 1 device. Then both must break.
    You do want pigtails, so if you change out device, neutral remains intact.
    Neutrals Need to stay together.
    lwchris's Avatar
    lwchris Posts: 16, Reputation: 1
    New Member
     
    #5

    Jun 9, 2007, 06:19 PM
    Quote Originally Posted by Stratmando
    Unless it is in 1 device.
    Please explain one device. Like a Split-circuit receptacle?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 9, 2007, 06:39 PM
    Yes split circuit on one device means two circuits on one receptacle. Only then will a 2 pole breaker be needed, both for residential and commercial.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Correction-GFI & AFI Breakers & Shared Neutrals [ 3 Answers ]

I need to submit a correction to some advice I had furnished in the past regarding Ground Fault and Arc Fault circuit breakers being used on shared neutrals. I had in mind the typical single pole 120 volt breakers that will not work if two breakers are used for two 120 volt circuits that share a...

Grounds and Neutrals under the same lug [ 3 Answers ]

Is it okay for a ground and a neutral wire to rest under the same lug in the main panel? If not, why? What are the potential dangers? Thanks in advance.

Using a 12/3 romex to provide 2 circuits in kitchen [ 2 Answers ]

What are the pro and cons of using 12/3 romex for 2 kitchen appliance ciruits. Of course there will be a GFIC on each circuit. Can this be done using the same neutral wire? Thanks in advance

Romex or bx [ 1 Answers ]

Hello, My niece is having some electrical work done in her hi rise condo, in manhattan NYC I notice romex cable being used, I always thought bx cable was code for NYC Any info is appr. Thank you

Neutrals and Grounds in service panel [ 2 Answers ]

I'm wiring everything for my basement in the panel. There are plenty of open spots left. When I look at the existing wiring (for the rest of the house), all the grounds go to the block on the left and all the neutrals go to the block on the right? 1. Is this required? 2. Why or why not? ...


View more questions Search