  • Jun 8, 2007, 11:15 PM
    lwchris
    Shared neutrals - two circuits on 12/3 romex
    I want to run two circuit with 12/3 Romex. Circuit #1 will be 3 light fixtures and circuit #2 will be two GFCI Receptacles. I am concerned about having shared neutral. From reading other post it is advised to splice all neutral and not use screw terminal to connect the two circuits. Also I will not be using the load side of the GFCI receptacles.
  • Jun 9, 2007, 01:50 AM
    tkrussell
    Shared neutrals are fine, still very popular in homes, thou a loose connection can cause some problems. Splicing at a device and not using screw terminals is not just wise advice, it is also required by code.

    Just be sure any splices up to the point the two circuits split off are good and tight, along with the connections in the panel, and you will not have any problems.
  • Jun 9, 2007, 05:40 PM
    lwchris
    Should I used a Double Pole Breaker. So that if one side of the breaker trips the other side will as well? Also is this OK in a commercial environment?
  • Jun 9, 2007, 06:05 PM
    Stratmando
    It can be on 2 single pole breakers.
    Unless it is in 1 device. Then both must break.
    You do want pigtails, so if you change out device, neutral remains intact.
    Neutrals Need to stay together.
  • Jun 9, 2007, 06:19 PM
    lwchris
    Quote:

    Originally Posted by Stratmando
    Unless it is in 1 device.

    Please explain one device. Like a Split-circuit receptacle?
  • Jun 9, 2007, 06:39 PM
    tkrussell
    Yes split circuit on one device means two circuits on one receptacle. Only then will a 2 pole breaker be needed, both for residential and commercial.