    Grounds and Neutrals under the same lug
    Is it okay for a ground and a neutral wire to rest under the same lug in the main panel?

    If not, why? What are the potential dangers?

    Thanks in advance.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 9, 2007, 01:58 AM
    It is only allowed if the lug is rated for more than one conductor. This rating will be listed in the manufacturers instructions and specs for any equipment.

    If not listed, then there is a chance the connection will not remain tight, or the connection is not correct. Loose connections can create heat that can damage equipment and cause a fire.

    An additional bar can be added to any panel, as each manufacturer offers optional extra bars when more lugs are needed.

    If the Main Breaker for your service is in this panel, then neutrals and grounds need to be together on the one neutral bar, but each wire should be under it's own lug. Neutral wires are considered as current carrying, and the equipment ground is a safety return.
    cafehyde's Avatar
    cafehyde Posts: 3, Reputation: 1
    New Member
     
    #3

    Jun 9, 2007, 03:27 PM
    Quote Originally Posted by tkrussell

    If the Main Breaker for your service is in this panel, then neutrals and grounds need to be together on the one neutral bar, but each wire should be under it's own lug. Neutral wires are considered as current carrying, and the equipment ground is a safety return.
    Thanks for the response tkrussell, that helps a lot. One more question: What can go wrong if a neutral and a ground are under the same lug? I understand that the neutral is current carrying, and the ground a safety return, but why is this unsafe?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jun 9, 2007, 06:40 PM
    The wires may come loose and the neutral wire can heat up.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sharing grounds between circuits. [ 7 Answers ]

My basic problem is that when I roughed in the wiring for the circuit that powers my smoke detectors, somehow I managed to use 14/2 between two of the boxes. Everything else was on 14/3 so I could inter-connect the alarms. Now, the last two aren't connected. So, I thought, why not use the ground...

Lug nut Torque [ 2 Answers ]

What would the lug nuts for my '93 Asuna be torqued to?

Lug tpye for 4/0 service cable [ 1 Answers ]

Does it matter what type lug I use or how its crimped if using a crimp type lug?. or is a allen head type lug OK? With or with out the ridgies that hold the wire tighter that some type have.. thank you... aluminum... 4/O

Garage main lug only height [ 1 Answers ]

Hi, just wondering if there is a minimum or maximum height for the main lug only box when surface mounted on a wall in a detached garage? I am running 40amps, 240V service underground to the garage. THanks in advance. Regards, Steve

Neutrals and Grounds in service panel [ 2 Answers ]

I'm wiring everything for my basement in the panel. There are plenty of open spots left. When I look at the existing wiring (for the rest of the house), all the grounds go to the block on the left and all the neutrals go to the block on the right? 1. Is this required? 2. Why or why not? ...


View more questions Search