    Junction box for #2 aluminum wire
    I need to join a new 100A feed on #2 aluminum wire to an existing #2 wire running from the panel. So this is actually #2 alum triplex in both cases plus a #8 bare copper ground. The junction will take place in an access panel in the wall where the two PVC conduits meet. What size junction box do I need for this? Is a juntion like this done with wire nuts the way a Romex juntion is? Does it matter what material the J-box is made of?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 17, 2007, 02:27 AM
    Use either an 8"x8"x6" or a 12"x12"x6" PVC box. Metal is OK, just have to connect a ground wire to it.

    Wirenuts are mot large enough for #2 wire. Need to use anything rated for #2 aluminum wire,such as split bolts with rubber and plastic tape. There are pre-insulated mechanical connectors available also. Be sure to use anti-oxidant compound on the wire connections.
    ptnoble's Avatar
    ptnoble Posts: 42, Reputation: 1
    Junior Member
     
    #3

    Apr 17, 2007, 10:18 AM
    Quote Originally Posted by tkrussell
    Use either an 8"x8"x6" or a 12"x12"x6" PVC box. Metal is OK, just have to connect a ground wire to it.

    Wirenuts are mot large enough for #2 wire. Need to use anything rated for #2 aluminum wire,such as split bolts with rubber and plastic tape. There are pre-insulated mechanical connectors available also. Be sure to use anti-oxidant compound on the wire connections.
    I don't think I have enough room for a 12x12 box so I would go with the 8x8 if that's acceptable. I found one that is 8x8x4. Do I really need the 6" depth?

    I was looking at PVC juction boxes last night in Lowe's and I notice that there are not pop-outs for access like there are for smaller metal J-boxes. Are you expected to drill an 1"1/4 hole into the side of these things? Does anyone have a recommendation on how to do this (hole saw bit for a drill?)?

    Also for #2 wire (Triplex) can I use 1" conduit or do I need 1"1/4?

    Thanks TK and others!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Apr 17, 2007, 01:03 PM
    The 4" is fine, just keep the wires as long as possible without crowding them,leaving room for the actual splices.

    You need a hole saw to cut knockouts out in a PVC box, if the conduit is 1-1/4" then need an actual 1-3/8" hole saw, or an electricians 1-1/4" .

    Use the 1-1/4" for the triplex and equipment ground.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Junction box as a cover? [ 3 Answers ]

I have a junction box currently that I need to add wiring to. It has the opening and internal clamps to add two more wires but this would put the box over its legal limit of wires in the box. The box is in a location that can be gotten at without removing any part of the building. The box is...

Junction Box Fill [ 5 Answers ]

I'm trying to find what the fill capacity on electrical junction boxes are. I found this chart The thing that is stumping me is do you count grounds or not? For example, the specific instance that has me looking is that I have a 4x4x1 1/4 box, with 4 12/2 cables in it. If you don't...

Joining wires in a junction box [ 1 Answers ]

In wiring a house, I have each room's wiring pulled to a junction box in the attic. Each junction box will be a circuit, with a home run going from the junction box to the panel. There are more wires than a single wire nut can join. Do I use jumpers to group the entire bunch so that that all...

Junction box question [ 2 Answers ]

Hello. I have a quick junction box question. Is there a limitation to the amount of wires I can safely join in a junction box? If so, what is it and are there regulations to what size box I can use? Thank you. I would like the have 8 wires (neglecting ground) in one junction box (1 in / 3 out)....

Junction Box size [ 2 Answers ]

I have and oven with 10/3 mc cable attached. I am going to splice this to a 10/3 romex cable that I pulled from the sub panel. Is a metal 3" deep single gang box big enough? How many cubic inches do I need? Thank you


View more questions Search