    Subpanel wiring
    Hello. I am helping someone build a house and I have a question about his subpanel. He has wired a subpanel in his garage "attached". He used aluminum #2 sec 2 conuctor with braided ground. I told him he needed 4 conductor because the ground and neutral must be separated at the subpanel. The next time I checked he had just run a bare # 4 copper wire he said he was going to use as ground and he is planning on using the braided aluminum wire as his neutral. This doesn't sound right to me. What say you experts. Thanks, Bud...
    ZCCG's Avatar
    ZCCG Posts: 20, Reputation: 2
    New Member
     
    #2

    Apr 14, 2007, 06:22 PM
    Bstrong,
    I can not give you an official answer but, I am an electrician and it sound like you are giving good advise to your friend. The braided wire should not be used as a neutral.
    It will require that the ground and neutral be separate at the Sub.
    If he would have pulled in a white wire of the correct size insyead of the bare copper wire, he just might have been able to get away with the braided wire as the ground.
    As for me... if this was my house, I would pull in a neutral(White) and still use the bare copper as a ground.
    Hopefully somebody else can give you a good answer to this question.
    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Apr 14, 2007, 06:33 PM
    The braided wire of SEC cable is allowed to be used as a neutral.

    Per NEC 2005 250.32(B) (2)
    The 3 wire is allowed, and must be connected at the subpanel end to the ground, but only if there is no other continuous metallic path between buildings, like water, phone lines, etc.

    This will be preferred over running any separate conductors, which is not allowed.

    A ground rod must be driven at the subpanel in any case.
    bstrong's Avatar
    bstrong Posts: 2, Reputation: 1
    New Member
     
    #4

    Apr 16, 2007, 05:14 AM
    Thanks guys for the help...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Subpanel in basement [ 1 Answers ]

I need three 20a circuits in basement. I planned to run #8 wire 50feet from main panel to a new sub panel in basement where I would have 3 20a breakers. Will this be OK or do I need #6 wire for the feed to the subpanel?

Need subpanel in basement [ 2 Answers ]

Hi, I am getting ready to finish my basement but my main panel is in my garage so I'm thinking it would make it easier for me if I install a subpanel in my basement. The main panel is 200 amp so I'd like to install a 100 amp subpanel. Is it okay to put in a 100 amp main breaker panel and feed...

Installing a Subpanel [ 3 Answers ]

I'm setting up a woodshop in my garage and want to install a subpanel to run my equipment off (it's going to be right next to the main). I'm starting from scratch, knowing extremely little about how to accomplish this. What sort of box do I need to buy, how do I size the breaker that will feed...

Grounding a subpanel [ 1 Answers ]

I have a set of direct current solar panels mounted on a metal structure (carport). All the panels and the structure are grounded to a ground rod driven near one of the support posts. Can I use the same ground rod for the ground connection of an alternating current subpanel mounted on one of...

Subpanel installation and wiring [ 1 Answers ]

I am constructing a wood working shop that is about 40 feet from my cabin in NC. The plan is to feed 240v 30amp from the main panel using 10/3 grounding outdoor wire. A subpanel will be installed in the shop with breakers for lights and outlets. The shop will contain a sander, grinder, drill...


View more questions Search