    200w robus induction hi bays tripping c/b
    I've recently installed 200 w induction hi bay lights in a factory. I have 12 on one contactor controlled via a switch. The lights are rated at 200 w each and I'm told they can run about 20 of them on the 20a cb so I should be well under.
    The problem is when I first go to turn the lights on they trip... but every time from the rest of the day... no problem? Any ideas?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Apr 10, 2014, 03:31 AM
    let's do some math, 200 watt fixtures X 12 fixtures = 2400 watts
    If the system voltage is 120 volts then the circuit is overloaded.
    If the system voltage is 277 volts then the circuit is about 50% loaded and I
    would start by swapping out the circuit breaker for a new one and see what happens.

    Just for fun, can you tell us what the voltage of the lights are?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Apr 10, 2014, 04:27 AM
    I tracked them down on the web. They are from Ireland. They use either 200 V @ 50 Hz or 240 V at 60 Hz.

    A string of 12 would be 2400 Watts (12 X 200 = 2400) and the amperage would be 10 Amps. (2400/240 = 10)
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #4

    Apr 10, 2014, 06:33 PM
    Inductive loads have a high in-rush of current until inductive reactance comes into play and the effective resistance goes up. Initially an inductive load has a near short circuit characteristic until the reactance comes into play. Not sure of all your details, but it sounds like it might be an issue.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #5

    Apr 10, 2014, 07:07 PM
    Quote Originally Posted by Studs ad View Post
    Inductive loads have a high in-rush of current until inductive reactance comes into play and the effective resistance goes up. Initially an inductive load has a near short circuit characteristic until the reactance comes into play. Not sure of all your details, but it sounds like it might be an issue.
    I needed to clarify a bit. In a/c circuits resistance is called reactance. Same basic concept as resistance is in DC circuits, except in DC circuits the resistance in a non rotating coil is constant with the circuit. In an AC coil(ballast) the resistance of the windings are very low until an AC voltage is applied. In industry a large transformer's greatest load is when it is first energized. It takes near short circuit current at that moment. After the initial loading the reactance of the AC component makes the resistance (reactance)to designed levels and the current drops. Your ballasts are basically a transformer and the in-inrush of current can be close to 7 times the operating current.

    How do you fix? If your wire size is sufficient to allow going to the next size breaker then do so. Industrial lighting can be up to a 30 amp breaker if my memory is correct.

    Or or eliminate some lights and put on another circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring diagrams for hampton bay 200w garden light transformer? [ 1 Answers ]

Can I use to leads from the transformer for the lights. I have a 200 Watt transformer with only about 80 watts of usage ?

Single-phase induction motor versus 3Phase-induction motor [ 1 Answers ]

I know the advantages of 3phase induction motor (IM) when compared with a single-phase IM one. However I need to justify using a single-phase IM (main and auxiliary windings) with a 3 legs inverter instead a 3phase IM with also a 3 legs inverter. Are the single-phase IM cheaper the 3phase one...

Hampton bays fan how to disassemble [ 3 Answers ]

Okay well I thought my fan broke because I went to home depot and they guy told me its not the remote since the tiny blinking light still worked on the remote. It was the box thing on the inside of the fan.. now I'm trying to change the box and I took off the light part and I'm on the part...

Hampton Bays outdoor lantern [ 2 Answers ]

Hello. We just purchased a Hampton Bays outdoor wall lantern at the home depot which is equipped with a photo cell and a sensitivity mode.I installed the Lateran exactly as directed and fellowed the instructions to set the mode to operate automatically. I set the sensitivity switch on the...

Hampton Bays ceiling fan [ 2 Answers ]

I just had a Hampton Bay ceiling fan installed. I have the remote control (It works) but I would prefer to use a wall switch to turn on/off the two lighted portions (St. Regis 60" fan, model #138498). The installer told me that "could not be done" because there is only one wire feeding power to...


View more questions Search