    How close can a wall be to an electrical load center?
    I'm wanting to build a wall perpendicular to a wall having a load center on it. How close can that wall come to the edge of that load center?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Mar 20, 2014, 10:30 AM
    What type of wall are you talking about?

    Working clearance requires a min. of 3'. So I wouldn't come any closer than that with the wall,
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Mar 20, 2014, 11:14 AM
    You must have 30" of clear width from side to side in front of a panel and a clear space of 36" in front of the panel. Maintain this and put your wall where you want...
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Mar 20, 2014, 11:50 AM
    The 30" side to side clearance is correct. Thing is, the panel can be anywhere in that 30" space. It does not have to be centered.
    So for instance, if there is 30" to one side, the panel can be right up against a perpendicular partition wall.
    athomas3171's Avatar
    athomas3171 Posts: 3, Reputation: 1
    New Member
     
    #5

    Mar 20, 2014, 01:08 PM
    Thanks!
    athomas3171's Avatar
    athomas3171 Posts: 3, Reputation: 1
    New Member
     
    #6

    Mar 20, 2014, 01:12 PM
    Quote Originally Posted by athomas3171 View Post
    Thanks!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Riser for T pan through slab but is too close to wall what can I do 60 mm from wall? [ 1 Answers ]

Recently I laid a drain for a toilet pan with a 100 mm riser through a concrete slab I have the riser 60 mm from the wall I know that's too close but is there any other options I can do before I smash up the slab any joints I can use??

What does 'invertible' load center mean? [ 2 Answers ]

In Siemen's literature, they state "13. All indoor Ultimate Load Centers are invertible for bottom feed applications." Does this mean that the panel can be flipped upside down so that the Main breaker is on the bottom (presumably allowed since the breaker On/Off is horizontal rather than...

How to support a load bearing wall, need engineer, cement wall [ 3 Answers ]

I want to remove about 6 feet from an interior wall. The rafters run parallel with the wall but the reason I think it's load-bearing is because one of the trusses rests on the middle of the wall with a lateral x across it. I have existing pictures and a drawing of "the existing" and what is...

Wiring load center [ 1 Answers ]

I have installed a new 200amp load center outside by my electric meter. Inside the load center the electric inspector told me that I needed 2 100amps to run to 2 separate moblie homes, so I did that. Now I am ready to run the wires they told me that I needed 3 wires and 1 ground wire, so I did...

Load Center Capacity [ 11 Answers ]

I have a new Square D load center installed rated at 100 amps. What does the 100 amp rating mean? If I replace the 100 amp main breaker with 200 amp breaker does that mean that The load center could melt if 200 amps flowed through it or that the incoming service wires could melt or what. Just...


View more questions Search