  • Mar 20, 2014, 09:08 AM
    athomas3171
    How close can a wall be to an electrical load center?
    I'm wanting to build a wall perpendicular to a wall having a load center on it. How close can that wall come to the edge of that load center?
  • Mar 20, 2014, 10:30 AM
    donf
    What type of wall are you talking about?

    Working clearance requires a min. of 3'. So I wouldn't come any closer than that with the wall,
  • Mar 20, 2014, 11:14 AM
    hfcarson
    You must have 30" of clear width from side to side in front of a panel and a clear space of 36" in front of the panel. Maintain this and put your wall where you want...
  • Mar 20, 2014, 11:50 AM
    stanfortyman
    The 30" side to side clearance is correct. Thing is, the panel can be anywhere in that 30" space. It does not have to be centered.
    So for instance, if there is 30" to one side, the panel can be right up against a perpendicular partition wall.