    What does 'invertible' load center mean?
    In Siemen's literature, they state "13. All indoor Ultimate Load Centers are invertible for bottom feed applications."

    Does this mean that the panel can be flipped upside down so that the Main breaker is on the bottom (presumably allowed since the breaker On/Off is horizontal rather than vertical)?

    If so, does it matter that the breaker numbering, stamped into the panel cover, reads upside down? I'll be covering these with labels anyway so I don't care...

    I like the idea, with a bottom feed, to have shorter (and out of the way) service feed wires.

    Tom
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 4, 2010, 01:33 PM
    Yes, invertible means the panel can be flipped to have the Main on the top or bottom, and the circuit legend will have two lists of numbers reversed so no matter which way the cover is installed it will be readable.
    TomWS's Avatar
    TomWS Posts: 26, Reputation: 1
    New Member
     
    #3

    May 4, 2010, 02:24 PM

    Great! Thanks again! BTW, if you're going to be near Belfast during the last 3 weeks of this month, hopefully I'll have the fruits of your wisdom to show off (plus I still owe you that scotch).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Square D load center ground bar? [ 10 Answers ]

I am installing a new load center and purchased a SquareD Home line box with a 200amp breaker. Service enters the house through a SquareD meter base that also has a 200amp main breaker. The meter base is attached to a single ground rod aprox 8 feet away. The new load center does not have...

Wiring load center [ 1 Answers ]

I have installed a new 200amp load center outside by my electric meter. Inside the load center the electric inspector told me that I needed 2 100amps to run to 2 separate moblie homes, so I did that. Now I am ready to run the wires they told me that I needed 3 wires and 1 ground wire, so I did...

Load Center Capacity [ 11 Answers ]

I have a new Square D load center installed rated at 100 amps. What does the 100 amp rating mean? If I replace the 100 amp main breaker with 200 amp breaker does that mean that The load center could melt if 200 amps flowed through it or that the incoming service wires could melt or what. Just...

Increasing my load center capacity [ 1 Answers ]

I have a weather proof CH main lug load center, grounded to earth, rated at 125 amps, with space for 4 breakers. I will be removing the 4 breakers and putting in a 100 amp breaker. From this 100 amp breaker, I will be running wires, less than a foot to a new CH 125 amp outdoor load center with 16...

LOAD center, scientific atlanta [ 1 Answers ]

I need a wiring diagram for a scientific atlanta load cent, series dcu-g1530or similar devise


View more questions Search