    Trane XL80 Can't Maintain Flame
    I have a Trane XL80 furnace. Basically, when it receives a call for heat, it ignites but cannot maintain the flame. As soon as the flame ignites (or within 10 seconds), it cuts off the gas flow and starts the ignition process again. It does this until the furnace locks out. Sometimes (probably 10% of the time) it maintains the ignition.

    Here is what is really strange. Three times I have had a service person look at it. They have replaced NOTHING and yet it seems to work when they get here and after they leave. Then a month or two later the same problem starts again. The service people even tell me, "I don't see any problems."

    Please help! I'm beginning to think my furnace is possessed.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 2, 2007, 04:08 PM
    Next time the person is out for service have them clean the flame rod/sensor if the unit has one.
    ryanod's Avatar
    ryanod Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 2, 2007, 09:15 PM
    Thanks for the response, but I've already cleaned the heat sensor. There is something else wrong.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Apr 2, 2007, 11:11 PM
    I am sure there is something else wrong but the problem is intermittent and thus hard to find. You will probably need to back track from the gas valva back to see what is the part that is causing the failure. This can be very time consuming. The next option is to start replacing parts but that is just far to expensive. See if there is a proving switch on the combustion blower assembly. That has also been shown to cause an intermittent problem.
    luap955's Avatar
    luap955 Posts: 1, Reputation: 1
    New Member
     
    #5

    Jan 23, 2011, 12:51 PM
    I had what sounds to be the same problem. I cleaned the flame sensor which is a small rod that extends out into where the flame shoots out. 1 screw and it comes out and there is a wire attached to it. Just take it out and sand it down some and reinstall. Hope this helps someone because I was a little worried about getting a big repair bill.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane XL80 TUD100R948K furnace [ 4 Answers ]

I have a Trane XL80 2 stage furnace just installed and in the manual it mentions that the blower motor speed can be adjusted by the spped taps wiring. It has 4 wires black, yello, red and blue. And there is a terminal called "PARK". Which has the yellow wire connected to it and then RED to LO HEAT...

Trane XL80 Heater Unit [ 4 Answers ]

We had a Trane XL80 Heater and XL 12 AC Condenser installed back in Jun 2004 - The blower fan on the heater is starting to make some noise! Not sure if it's getting ready to go out? Or not - also we had a Sta-Med Electronic Air Cleaner installed at the same time - the power light (green) does not...

Trane Xl80 Furnace [ 1 Answers ]

Hi, Keep getting the blinking light on the control panel. Flashes 4 times it say's it means that the thermal protection device is open. O.K. what does that mean . And can I fix or do I have to call a repair man Thanks Jimmyd

Trane XL80 blower problem [ 3 Answers ]

I have a Trane XL80 furnace, about 16 years old, with heat only setup. After we turned on the heat, the pilot fire came on, then the furnace lit and the heats up, however the blower wasn't turning and not blowing air. We opened both doors, saw the fan limit (a little round dial with setting to...


View more questions Search