    Air handler blower will not come on
    Twisted the green and red wires together on the thermostat, t and the blower came on, what does this mean?
    A-Cguy602's Avatar
    A-Cguy602 Posts: 5, Reputation: 1
    New Member
     
    #2

    Jan 15, 2014, 06:14 PM
    All you did was bypass the thermostat, making it run in "fan only" mode.

    If the thermostat was not responsive I would suspect you have a bad thermostat or it is programmed incorrectly (switches on back of t-stat).

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air handler blower always running [ 1 Answers ]

I have a heat pump outside with indoor attic air handler. I don't use it very often. I tested it and found that the system seems to work when I turn the temperature up on the thermostat but when I turned it down again to shut the unit off, the heat pump turned off outside but the fan blower always...

Blower will not run on my Air handler. [ 3 Answers ]

24 volts to T- Stat but blower will not come on. The 5 amp fuse in the air handler is good and the outdoor unit runs and the coils in the air handler get very cold but the blower will not come on. I have jumpered the red and green wire and nothing. I jumper the red and white wire and the heat comes...

Air handler blower motor [ 6 Answers ]

At night I run just the fan motor with no climate control. I do this because the white noise of the compressor drowns some of the noise out from my inconsiderate neighbor upstairs. Will I be consuming a lot of energy? Does this run off 220? I don't want a huge bill at the end of the month but until...

Air Handler blower won't [ 10 Answers ]

I have a 3 1/2 year new AMANA GUIV070FX40 attic mounted system that is the furnace / air handler for an AMANA RCE42C2A condenser / compressor. The entire system, including new ducting and separate electrical circuits (220 for the compressor / 110 for the air handler) was installed by a credible /...

Air Handler Blower [ 2 Answers ]

One of the 3 brackets that attaches the fan motor to the blower housing on my inside a/c unit has broken, causing the motor to tilt to one side. I pulled the blower and tie-wired the motor to the housing and it seems to be holding. Hopefully this will last a few days. I could adapt a...


View more questions Search