        Homeline 200 amp buss bar loose.
       
                  
        Lights flicker etc. on a  few  circuits. I traced it to the buss bar where the 200 amp main braker is bolted to the buss bars. I can  hear  it sizzle when its arcing  up. It  was installed in 2007 by a licensed electrician, 200 amp square D home line. 
 If I clean  it is  there a juice I can put on  it?  Where its  bolted between the  buzz bar and the breaker tab, is that a stud or a nut and bolt?
 
 Yes, I know to turn the main breaker off. I got no answers or help yet. However, if  I clean where its  bolted and add the No Ox  stuff, will that help?
 
 Thanks... richard
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Nov 3, 2013, 07:20 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I will assume you mean buss bar. Hard to imagine how it could just come loose. With main breaker off, just tighten down but remember, it is still hot above the main breaker.
     |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 4, 2013, 05:17 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Yes... I  did  that... it  helped  a  day  or  so... but  I  think it  needs  cleaning because  of  the  arking  that  was  done... and  some  no  ox  stuff  put  on  it... did  you  ever  use  the  no  ox  stuff ?Tks... richard
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 4, 2013, 05:30 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        The main circuit breaker in your panel is arcing and you're guessing?A real professional needs to look at this as this is how many home fires begin so it needs to be repaired or replaced, Now!
 (antioxidant is not a cure)
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 4, 2013, 06:14 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        No.. I  am  not guessing... when  the  lights  are  frickering... I  can  hear  it  sizzing... when I turn off the  affected  15 amp  breaker.. the  sizze  stops   and  starts  again  when  turned  on... however... re  tighten  helped  a  little.. it  was  installed  in  2007... are  you  sure  that  cleaning  and  adding  the  no  ox   won't  help ?   So... what  is  a  fix ?   New  whole  200 amp  box  with  a new  main ?Or  new  bus  bars  and  a  new  main ? Thanks... richard
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 4, 2013, 06:23 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        What is a fix? Difficult to know from here... obviously this is beyond your experience so I recommend hiring a professional to look at the panel. Personally, I would be expecting a new panel.
     |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 5, 2013, 05:58 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by hfcarson   What is a fix? Difficult to know from here... obviously this is beyond your experience so I recommend hiring a professional to look at the panel. Personally, I would be expecting a new panel. A new  panel? lol... a good license  electrician installed  this  in 2007.. maybe  it  was  not torqued  proper. I know  this could be  serious  but  I  also  think  it's a  minor  fix... waiting on  the electrician to call me  back.. he  is working  60 miles away  and very  busy... iretighten  the  bolts.. seems  to  be  OK  now... however... because  it  was  arcing   can I  unbolt... clean.. sand.. and  add  some  no ox stuff.. re torque? yes   I know  to  turn  off  the  main  breaker 
Hank  you... richard
     |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 6, 2013, 07:19 PM
                  
                 |  |  
  
    | 
        
        
        
       
        
        What is the better 200 amp load center
       
                  
        I guess they are all pretty good  but I favor  the  square d   Or the square d home line.. is the oringial  smaller  breaker  square  better ?  I know  they cost more... but are  they  better... tks... richard
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Nov 6, 2013, 09:38 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        For most regular applications a Square D homeline is fine. Value package and inexpensive breakers. Buss bars are aluminum but then, so is the service entrance cable. Have never seen one go "bad ".
     |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Nov 7, 2013, 05:38 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        IMO for a residential panel none is any better than the rest. I am not a fan of SquareD, so I do not buy into the whole "SqD QO is top of the line" hype.
 Many people hate GE panels. I actually really like the layout of them.
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 20, 2013, 07:48 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I could  hear  it  sizzle  a  little   no  sparks  or  nothing... just  a  small  sizzle... I think its OK now.. but  not for sure how long... a  lot  easier  to  replace  the  2  bus bars  and a  200 amp  main... then  the  whole  box... are  the   hot  bus bars  available  to  buy ?   Maybe buy  a  whole  box  and  swap  then  out  along  with  the  new  breaker ?Thanks... richard
 
 I have a sub 14  space panel in the garage.. no  main.. just  the  hots go into the main lugs... can I  use  a  220  30 amp breaker at the top as a main ? With the hot wires feeding the 220 v 30 amp  breaker?. I  have  10--3  running  to  the garage
 Ground is not boned to the common... I  have a ground rod outside  for  the  ground... tks
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 20, 2013, 08:18 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Unless your local power company allows you to pull the meter (Their equipment) you really should not attempt to fix this.
 The meter must be pulled to kill the power to the panel, then you must tighten the screws according to the torque requirements set by the manufacturer of the panel.
 
 If you try to do this on a live panel, you could end up dead or severely burned.
 
 I suggest you get a licensed electrician for this work, it is really not a DIY project.
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 20, 2013, 09:30 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        You can't do this... you will violate the assembly listing, void the warranty, etc.I doubt square D would even sell you the parts...
 Buy a new panel...
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 20, 2013, 11:46 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks to a correction note I just received, I need to amend my original post.
 The panelboard in question is governed by Article 408, not the Main Services Panelboard.
 
 The overcurrent protection must be on the supply side of the panelboard.  The six-switch configuration does not apply to this panelboard.
 
 If the panelboard if fed by taps, the protection must be a main breaker within the panelboard.  If the feeder is protected by breakers or fuses on the supply side, you should be fine, however it will still be prudent to put in a disconnect switch on the supply side of the garage's panelboard in case of an emergency.
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Full Member |  | 
 
                  
                      Nov 21, 2013, 11:52 AM
                  
                 |  |  
  
    | 
        
        
        
       
        
        What  holds in my 200 amp  main
       
                  
        200 amp homeline.panel.. in stalled  in  2007.. I  need  to  turn off.. unbolt  the  200 amp main  from  the  hot bus bars  and  clean.. I  can't  get  then  tight  maybe  some  pitting  from  the  lights  flickering
 Main question... what  holds in the  main... looks  like  one  big  screw  in  the  middle... thank  you
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Nov 21, 2013, 12:54 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Even if you turn the panelboard off (by way of the main breaker) the feed lines to the panelboard and their mounting lugs will still be hot!
 I'm hard pressed to understand why you are so intent on getting yourself injured!
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
	
		
	
	
  | 
    
      
                |  | Ultra Member |  | 
 
                  
                      Nov 21, 2013, 01:01 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I agree with Don here, there are no user serviceable parts here... There is obviously something wrong and it sounds like you want to make guesses as to the solution and maybe get lucky...
 Sorry, but again I will advise you to just replace this panel before something unhappy occurs...
 |  
    | 
      
      
      
      
        
      
            
      
        
      
      
      
     |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 
 
Check out some similar questions!
Buss bar
 [ 14 Answers ]
When adding a neutral/grounding buss bar to the main panel how do you connect to the existing bar. I was told at home depot to just butt them edge to edge.
 
Netural buss bar grounding
 [ 4 Answers ]
My nephew owens a small cabin in the woods w. no electrical service. He is using a generater in the daytime and a battery/ inverter set up at night. I have installed of course a dpdt transfer switch to switch between the two sources. Im going to put one small branch circuit in the cabin which will...
 
HOT Temp buss bar 100A House Service panel
 [ 6 Answers ]
In replacing a 15A circuit breaker found that one of the buss bars is getting very hot. 
Before connecting, installing breaker only, buss bar is hot enough to heat up the breaker? 
Probable causes?  There are more breakers on one buss side, unbalanced load.
 View more  questions